Cause of constant 'Battery Low Chemistry Voltage' alerts on new UPS/battery strings

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cause of constant 'Battery Low Chemistry Voltage' alerts on new UPS/battery strings
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
11
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

Cause of constant 'Battery Low Chemistry Voltage' alerts on new UPS/battery strings

We have two EPS 6000's with four strings of batteries for each and battery monitors connected to each string.  We seem to get a lot of alerts that say string discharging from each string and sometimes see the voltage on some of the batteries drop from 13 volts down to 7 or 8 volts then jump back up over the course of a few minutes. The other alarms we get(but no where near as often) are Battery Low Chemistry Voltage, Disconnected Battery or Dryout or Sulfation Condition Exists.  Has anyone seen these errors before with this type of setup?  We have had multiple people go over the system and they cannot seem to find anything wrong and have had the batteries pass testing.

Any insight would be appreciated.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:29 AM

I spoke to the case owner today and he said he has not seen the UPS logs so they have not been forwarded or reviewed by all involved just yet.

Anyway, he seemed to indicate that for some reason, there was a discharge on every single battery so maybe the problem was that there was a discharge but the UPS did not log it?

Someone is going to the site soon though to review it more closely but we really feel there was something that happened to discharge the strings and that everything else on the system looked good and normal.

Unfortunately, to the fault of those that designed the alarm text, some things come across as "alarms" but are more so informational and that might be happening here.

I am not sure on the battery specific questions either though myself. (like how much voltage the voltage should drop) I assume it will depend on how much current/load on them?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

Is this by using your APC Battery Management System (AP9921X) or are these alarms directly from the UPS?

If this is from a Battery Management System - the first thing we always check to validate any alarms is if the user has done a calibration on the system so that we know we are not getting false alarms/readings. If you want to FTP to the AP9921X BMS and get me the config.ini, event.txt and data.txt files, I can see if it has been done. (Instructions on getting log files are here in the knowledge base -> http://www.apc.com/site/support/index.cfm/faq/ -> search for article ID FA156131)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

I have the files but would prefer not to post them on the forums, is there an email address i can use to send them to you?  We actually had APC install and configure the units and have had techs come out multiple times to check them but have yet to find a cause for the alarms.  We have been told that these battery monitors are used by other clients with the same UPS  system we have and they do not have the same issues we are experiencing. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

Do you already have a case in progress for this issue then where the logs are already available before I make you send them again? (also, I assume then this confirms it is a battery management system we are talking about here?)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

Our Facilities department opened a case but I do not have the number, I believe August Patrick is involved in the case, I will see if I can get the case number later.  I think my biggest issue is right now I don't think I fully understand how the UPS and the battery monitors interact with the batteries and what could cause them to show batteries at 12 volts that drop to 8 volts then jump back up to 12 in under a minute.  Sorry if this is very vague, I don't think I know enough about the system to know the right questions to ask.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

To be honest, my weakness is batteries in general and I am good with the battery management system management card side and some of the specifics of how it works but maybe between us we can identify what is going on where the case is smile

If you cannot get the case number, I'll do a little more searching in our database and if I can't find anything, I'll tell you where to send logs.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

I did find some cases from earlier this year but it'd be good to verify the on going case number so I don't duplicate efforts after understanding who is managing the case and what they're doing. From logs I did see, the systems have been calibrated but I have not verified that per the manufacturer's suggestions, battery cell voltages are setting according to their mins/max. That might be a moot point but I usually just ask these questions methodically, like I said, to ensure the alarms/values are accurate for the situation.

Many users of the BMS are in the same boat unfortuantely as far as understanding of the product because of the fact that the system shows "alarms" which probably should be reworded as "informational events" so this may not even be an alarm but more of an FYI.

Regardless, once I get a case number or more info on what August is working on and with who, I can try to help too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

It looks like the current ticket is C1-4828119591 and the last previous ticket was C1-4641970090.  The last response was that they believed the alerts to be due to power bumps however the UPS doesn't show power bumps at the same times and it doesn't explain the extremely low drop in voltage on some of the battery managers that it is reporting faulty batteries for a minute.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

Ok, I only saw C1-4641970090 before which did not really indicate the answer was not appropriate so it seemed pretty cut and dry to me. C1-4828119591 I do see that someone is going to go out to the site?

Anyway, the notes in the newest case indicate: the times on all the BMS are not synced, but based on the times these logs were downloaded which was probably close in time, both units  do show a power blip.  All the BMS on UPS A went at the same time and all the BMS on UPS B went at the same time.  This is an indication of a quick power blip.

Were they given the UPS logs to look at or I am just confused as why they would think this but you do not. I'll also follow up with the case owner as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

I just sent those in last night, they never asked for them before from me but they were working with a member from our facilities team who isn't with us anymore and were also on site multiple times.  The battery managers is sending us alarms that a battery dropped from 13.1 volts to 8 and back up to 13.1 in less than a minute is not possible for a healthy battery which I was told by the on site APC tech and our Facilities members.  The batteries were new when installed and have been tested by APC and have not had any fail testing. How much should the voltage drop when the UPS switches to battery?  On one hand we are told the batteries shouldn't drop to such a low level like that, but on the other we are told they are normal power bumps - that is why i would say it's not a good answer to our issue.

The BMS are set to use our NTP server with the same settings that our rack PDU's are using and the rack PDU's do not seem to have any issues keeping in sync.  No idea what to do with this issue

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:54 AM . Last Modified: ‎2024-03-19 12:29 AM

I will check into it further. I did not hear back from the case owner yet and have been tied up all afternoon.

The battery part is what I am weak with as well, especially on a 3 phase application. I would think that if the UPS went to battery then there was current draw which could've drawn the voltage down. That is all I know at a high level embarassed

I will follow up more tomorrow smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:29 AM

0 Likes
0
2214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:29 AM

I spoke to the case owner today and he said he has not seen the UPS logs so they have not been forwarded or reviewed by all involved just yet.

Anyway, he seemed to indicate that for some reason, there was a discharge on every single battery so maybe the problem was that there was a discharge but the UPS did not log it?

Someone is going to the site soon though to review it more closely but we really feel there was something that happened to discharge the strings and that everything else on the system looked good and normal.

Unfortunately, to the fault of those that designed the alarm text, some things come across as "alarms" but are more so informational and that might be happening here.

I am not sure on the battery specific questions either though myself. (like how much voltage the voltage should drop) I assume it will depend on how much current/load on them?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of