Dear all,
I'd like to change some configuration details - especially SMTP and email recipients - on my Smart-UPS RT 6000 RM XL but anything I configure is discarded. No matter I use the web or the console. I updated to the latest firmware but still no changes can be made.
I'm logged in as Super User (apc).
Card Model: AP9631
Hardware Revision: 05
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:27 AM
Hi Philipp - glad to hear. And thank you, hope you have a nice Easter weekend too!
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM
Hi Angela,
thanks for your suggestion.
The problem finally was solved by formatting the flash memory.
Now all configuration can be made and persists.
Have a nice Easter-Weekend! 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:27 AM
Hi Philipp - glad to hear. And thank you, hope you have a nice Easter weekend too!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.