Posted: ‎2025-02-26 10:43 AM
Hi:
I installed a new APC UPS SMT1500RM2UNC. It has a network card that I connected to my network. I can see it on the network and ping its IP, which it must have obtained via DHCP. However, when I enter the IP into a browser tab, it responds: Hmmm ... can't reach this page. xxx.xxx.xxx.xxx refused to connect.
Also, it's not accepting telnet connection.
How to connect to UPS so I can manage it?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-02-27 05:19 AM
Hi IT_Tro,
if you have connected the UPS through the SmartConnect port (you recognize it because it's super green with a Cloud icon), then you won't have any Web UI, as you need to use smartconnect.apc.com portal to manage it.
If, instead, you installed/have preinstalled a dedicated NMC card in the slot, you should connect to that.
Attached a picture with highlighted the 2 Eth ports.
Have a nice day!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-02-26 09:25 PM
What network card is installed into the unit and is it brand new vs used? If this is a brand new AP9640 / 41 NMC.
Insure you use HTTPS vs HTTP.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-02-27 05:19 AM
Hi IT_Tro,
if you have connected the UPS through the SmartConnect port (you recognize it because it's super green with a Cloud icon), then you won't have any Web UI, as you need to use smartconnect.apc.com portal to manage it.
If, instead, you installed/have preinstalled a dedicated NMC card in the slot, you should connect to that.
Attached a picture with highlighted the 2 Eth ports.
Have a nice day!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-05-21 02:14 PM
Hi @Taorming :
Turns out these units do not have NMC cards, thus need to manage using the SmartConnect ports.
The QR code I found on the back gives me the MDL and S/N. But when I try to register at smartconnect.apc.com, it's asking for Product ID and Product Key. Is there supposed to be another QR code somewhere on the unit?
Thank you.