Cannot Update Firmware in AP9630 NMC2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cannot Update Firmware in AP9630 NMC2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
bimmerdriver
Lieutenant JG bimmerdriver
Lieutenant JG

Posted: ‎2025-04-19 01:36 PM

0 Likes
7
464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-19 01:36 PM

Cannot Update Firmware in AP9630 NMC2

I'm trying to update the firmware in my AP9630 NMC2, which is Hardware Revision 05. I've updated the firmware previously without any difficulties. FTP is enabled and I can connect to the unit using WinSCP.

 

The unit currently has the following firmware installed:

Application Module
Name sumx
Version v7.1.2
Date Mar 21 2023
Time 17:44:20
APC OS (AOS)
Name aos
Version v7.1.2
Date Mar 21 2023
Time 17:34:00
APC Boot Monitor
Name bootmon
Version v1.0.9
Date Mar 27 2019
Time 16:23:06

 

The update I'm trying to install is: apc_hw05_aos718_sumx718_bootmon109.

 

The updater generates two files:

 

update.txt:

[04/18/2025 13:34:02] NMC Firmware Update Utility v1.0.4 initialized.
[04/18/2025 13:35:10] Downloading and verifying configuration file from 10.28.92.150, please wait...
[04/18/2025 13:35:11] Firmware distribution does not match target device platform; this could be due to a corrupt distribution.
[04/18/2025 13:35:11] Uploading firmware file 1 of 3: Boot Monitor to 10.28.92.150, please wait...
[04/18/2025 13:35:11] Unable to update device 10.28.92.150 with Boot Monitor; stopping all further processing of this device!

 

error.txt:

[04/18/2025 13:35:11] Firmware distribution does not match target device platform; this could be due to a corrupt distribution.
[04/18/2025 13:35:11] Unable to update device 10.28.92.150 with Boot Monitor; stopping all further processing of this device!

 

The files unzip without error, so I doubt there could be any corruption unless they were corrupted before the zip file was created.

 

The unit is the supported type and hardware revision, so I also doubt there is an incompatibility.

 

I tried using SCP and FTP. There was no difference.

 

The aos and sumx files from the previous update are in /root.

apc_hw05_aos_712.bin

apc_hw05_sumx_712.bin

 

I did not try to update the firmware using FTP. I don't want to brick it.

 

Has anyone else encountered this problem? If so, what is the work-around?

 

Thank you.

  • Tags:
  • english
  • NMC2 AP9630 FIRMWARE
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
bimmerdriver
Lieutenant JG bimmerdriver
Lieutenant JG

Posted: ‎2025-04-24 03:02 PM

0 Likes
1
310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 03:02 PM

I thought I would check one last time for a new version of firmware before I tried reformatting the NMC. To my surprise, there was a new version. I downloaded it and the release notes. I was hoping to see some reference to upgrade failures similar to what I encountered, but there weren't any. I tried again, using SCP, and it failed in the same manner as the previous version. I tried again using FTP and it worked. I suspect there is a problem in the firmware update utility. Anyway, I now have the latest firmware in the NMC.

 

Thank you for your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Teken
Spock Teken
Spock

Posted: ‎2025-04-22 03:33 AM

0 Likes
2
444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-22 03:33 AM

What specific model APC UPS (SKU) is the NMC installed on?!? Provide a screen capture of the About tab for both UPS / NMC here.

 

Are you using the NMC firmware wizard vs trying to upload the individual files via CLI??? You should be using the guided wizard and once the credentials / IP Address have been entered select FTP and do (NOT) save logs than proceed. 

 

NOTE: Validate on the (LCD Menu) that communications have not been disabled: Serial, Modbus, NMC. This normally affects the ability to load UPS Firmware vs NMC Firmware.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

bimmerdriver
Lieutenant JG bimmerdriver
Lieutenant JG

Posted: ‎2025-04-22 02:31 PM

In response to Teken
0 Likes
1
412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-22 02:31 PM

Thank you for your reply.

 

Here is a screen capture the UPS from the NMC:

bimmerdriver_0-1745356262837.png

 

Here is a screen capture of the NMC from the NMC:

bimmerdriver_1-1745356328207.png

 

I have PCNS V5.1 installed.

 

Here is a screen capture of /root on the NMC:

bimmerdriver_2-1745356468842.png

 

As you can see, there is not a copy of the bootmon file in /root (or anywhere else that I could see).

 

I tried installing the firmware using apc_hw05_aos718_sumx718_bootmon109. I have tried both SCP and FTP. It fails the same way in both cases. Backup log files prior to update is disabled.

 

I have updated both the UPS and the NMC firmware previously with no problems.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-04-23 04:18 AM

In response to bimmerdriver
0 Likes
0
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-23 04:18 AM

Please refer to this APC FAQ as it relates to alternative methods of upgrading the NMC:

 

https://www.apc.com/us/en/faqs/FA156047/

 

Before doing so have you tried different web browsers and computers?!?

 

Also, if you had a AP9631 you could have used the USB port to upgrade the hardware. ☹️ 

 

Lastly, as a sanity check you may consider formatting the NMC to a default state. Disconnect the Ethernet cable, press and hold the reset button until you see the orange LED flash (approximately 20+ seconds), than release.

 

Reconnect the Ethernet cable . . . 

 

It will take approximately 1-2 minutes for the NMC to format the system. Once complete the system will be in a OEM / default state and DHCP will be enabled.

 

Formatting the NMC has no impact on the UPS. This suggestion is to bring the NMC to a known state in case it’s in a unknown state.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

bimmerdriver
Lieutenant JG bimmerdriver
Lieutenant JG

Posted: ‎2025-04-23 08:38 PM

0 Likes
1
353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-23 08:38 PM

Thank you for your reply.

 

Since the AP9630 doesn't have a USB port and I don't have a serial cable, I will try ftp next. Before I do so, I have a couple of questions.

 

First, regarding contents of the /root directory on the unit, as you can see from the screen capture, only the aos and sumx binaries are present. They are the same versions that are installed. Is there a reason why the bootmon binary is not also in present in /root? It seems inconsistent if the aos and sumx binaries remain in /root but not the bootmon binary.

 

Second, even though the latest firmware update does not change the version of the bootmon binary, should I try reinstalling bootmon first?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-04-24 03:12 AM

In response to bimmerdriver
0 Likes
0
343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 03:12 AM

Personally I would see what happens on another computer / web browser first. Followed by formatting the NMC as outlined earlier than try to update the NMC using the software upgrade utility.

 

If both fail to update the NMC you can proceed to use FTP. So you can follow the APC FAQ and reload the bootmon first followed by the remaining two files as outlined by the FAQ.

 

Lastly, to be clear the user credentials being used is indeed a Super User?!?! 🤔

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

bimmerdriver
Lieutenant JG bimmerdriver
Lieutenant JG

Posted: ‎2025-04-24 03:02 PM

0 Likes
1
311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 03:02 PM

I thought I would check one last time for a new version of firmware before I tried reformatting the NMC. To my surprise, there was a new version. I downloaded it and the release notes. I was hoping to see some reference to upgrade failures similar to what I encountered, but there weren't any. I tried again, using SCP, and it failed in the same manner as the previous version. I tried again using FTP and it worked. I suspect there is a problem in the firmware update utility. Anyway, I now have the latest firmware in the NMC.

 

Thank you for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2025-04-25 04:51 AM

In response to bimmerdriver
0 Likes
0
301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-25 04:51 AM

That’s great to hear and please do mark the reply I suggested as a solution. So it may help the next person asking the same. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of