Can't seem to connect 9617 to apcupsd

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can't seem to connect 9617 to apcupsd
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
140
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
14
4920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

Can't seem to connect 9617 to apcupsd

I'm running UnRaid and trying to get it to connect to my 9617. The settings look right in the apcupsd  .conf file based on reading the manual, but it just won't connect. ApcTest returns can't connect to socket (38). I ran netstat and I don't see any other resources hogging the port, but I don't see the daemon using the port either I almost think it's an authentication problem, but I reset the Device name and Device password (not user password).

Anyway to test the device name and device password to make sure it's correct? Any other bright ideas?

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apcupsd
  • device
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

I never could get PowerChute to see my UPS, I assume that was also a password issue. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

OK, when i try to log into the Device (not user) I get protected object. Which setting in the interface is causing this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

Is the "device" user enabled within the AP9617 preferences?

On SUMX 3.7.2/AOS 3.7.3 this is located under the Administration tab > Security > Local Users > Administrator, Device or Read Only.

Is HTTPS enabled in the management card's configuration interface? (Administration tab > Network > Web > Access)

Another setting to check might be that regarding authentication. (Administration tab > Security > Remote Users)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

On 1/30/2016 8:19 PM, William said:

Is the "device" user enabled within the AP9617 preferences?

Yep

On 1/30/2016 8:19 PM, William said:

On SUMX 3.7.2/AOS 3.7.3 this is located under the Administration tab > Security > Local Users > Administrator, Device or Read Only.

Read Only is enabled, what is this for?

On 1/30/2016 8:19 PM, William said:

Is HTTPS enabled in the management card's configuration interface? (Administration tab > Network > Web > Access)

HTTPS was off, HTTP on. I changed, but it did not make a difference

On 1/30/2016 8:19 PM, William said:

Another setting to check might be that regarding authentication. (Administration tab > Security > Remote Users)

Only local authentication is turned on. I thought this would be OK for the LAN.

I was able to get into the Device through the browser, PowerChute on my PC was blocking it. I was hoping this would solve my UnRaid problem too, but it did not. 😞

Thanks for the help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

Hi,

Go the the Administration tab - General - Reset/Reboot and Reset All Except TCP/IP to reset the NMC to factory defaults. Then configure APCUPSD to communicate with the card.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

On 1/31/2016 10:00 AM, Bill said:

Go the the Administration tab - General - Reset/Reboot and Reset All Except TCP/IP to reset the NMC to factory defaults. Then configure APCUPSD to communicate with the card.

Tried that twice. 🙂 Updated the firmware too. The status on the card is OK.

I also installed APCUPSD in Windows with the same result. I added my boxes to the client list on the card, switched back to DHCP, added the APC to my hosts file in Windows/Linux. 

I can get into the admin/device with the browser and the console. I can also ping the IP and the friendly name. Going to try pinging (nping) the port next to see if it's being blocked.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

apctest returns this:

2016-01-31 13:19:21 apctest 3.14.13 (02 February 2015) slackware

Checking configuration ...
sharenet.type = Network & ShareUPS Disabled
cable.type = Ethernet Link
mode.type = PCNET UPS Driver
Setting up the port ...
apctest FATAL ERROR in apctest.c at line 321
Unable to open UPS device.
If apcupsd or apctest is already running,
please stop it and run this program again.
apctest error termination completed

What is this about? sharenet.type = Network & ShareUPS Disabled

I can't find a setting for it.

apcaccess returns this:

root@TerraByteMe:/etc/apcupsd# apcaccess status
APC : 001,018,0465
DATE : 2016-01-31 13:22:28 -0500
HOSTNAME : TerraByteMe
VERSION : 3.14.13 (02 February 2015) slackware
UPSNAME : TerraByteMe
CABLE : Ethernet Link
DRIVER : PCNET UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2016-01-31 13:22:19 -0500
STATUS : COMMLOST
MBATTCHG : 10 Percent
MINTIMEL : 10 Minutes
MAXTIME : 0 Seconds
NUMXFERS : 0
TONBATT : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
STATFLAG : 0x05000100
END APC : 2016-01-31 13:23:19 -0500

It does seem to see the UPS, as it shows this: APC : 001,018,0465

Any ideas?

Thx

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

Hi,

Ran a test this morning and was able to get communications established between APCUPSD version 3.14.13 on Windows 7. The NMC was a AP9618 running AOS 3.7.3 and SUMX 3.7.2 Be sure to enter the proper ip address of the NMC, user name, and pass phrase in the config file. The defaults the user name is apc and the pass phrase is admin user phrase. You should also verify UDP port 3052 is open on the system and not blocked on the LAN and that the ip address of the system is registered with the NMC. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

On 2/1/2016 11:22 AM, Bill said:

user name is apc and the pass phrase is admin user phrase

So my firmware and APCUPSD version are the same as yours, Servers are entered in the NMC client.

The original firmware had Device User, Device Password and Device Pass Phrase. The new firmware only has User and password. I changed both of these and can log into the device user from the browser.

The odd thing is that PowerChute cannot detect the card either, so it looks like a port issue, just strange that it's happening on a Linux Box and a Windows box. That pretty much leaves the router. I guess I'll connect the card to a crossover cable on the laptop and see what happens.

The IP utility by APC does find the card though.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

Hi,

You should also verify the authentication phrase matches. The default is admin user phrase. If the phrase does not match communications will fail.

In apcupsd.conf be sure 

UPSCABLE ether

UPSTYPE pcnet

DEVICE XXX.XXX.XXX.XXX:apc:admin user phrase

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:54 AM . Last Modified: ‎2024-03-13 04:32 AM

I think we have a winner! Thanks.

smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:32 AM

Still no joy.

Config looks like this:


UPSNAME APC961702

UPSCABLE ether

UPSTYPE pcnet

DEVICE 192.168.1.124:APC9617:################

SCRIPTDIR d:\apcupsd\etc\apcupsd

PWRFAILDIR d:\apcupsd\etc\apcupsd

NOLOGINDIR d:\apcupsd\etc\apcupsd

ONBATTERYDELAY 6

BATTERYLEVEL 5

MINUTES 3

TIMEOUT 240

ANNOY 60

ANNOYDELAY 120

NOLOGON disable

KILLDELAY 0

NETSERVER on

NISIP 0.0.0.0

NISPORT 3551

EVENTSFILE d:\apcupsd\etc\apcupsd\apcupsd.events

EVENTSFILEMAX 10

UPSCLASS standalone

UPSMODE disable

STATTIME 0

STATFILE d:\apcupsd\etc\apcupsd\apcupsd.status

LOGSTATS off

DATATIME 0

#FACILITY DAEMON

#BATTDATE mm/dd/yy

#SENSITIVITY H

#WAKEUP 60

#SLEEP 180

#LOTRANSFER 208

#HITRANSFER 253

#BEEPSTATE T

#LOWBATT 2

#OUTPUTVOLTS 230

#SELFTEST 336

Still getting this:

APCUPSD Tray

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:32 AM

0 Likes
0
4916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:32 AM

On 2/3/2016 8:31 AM, Bill said:

DEVICE XXX.XXX.XXX.XXX:apc:admin user phrase

dang, missed this bit. Apparently it ignores the Device name and uses apc no matter what.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

0 Likes
0
4916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

I had similar issues with 9617 and apcupsd on Mac OS X. Verified using the Powerchute software that username and passphrase matched but still couldn't get apcupsd to work. In the end I've switched to using Powerchute which is actually quite decent in terms of functionality, although I wish it had some kind of menubar monitor. I guess that may not help in your case though.....

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

0 Likes
0
4920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

I never could get PowerChute to see my UPS, I assume that was also a password issue. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Š 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore