Can't find some MIBs in MGE Galaxy 5500 UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can't find some MIBs in MGE Galaxy 5500 UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:16 AM

0 Likes
9
2715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:16 AM

Can't find some MIBs in MGE Galaxy 5500 UPS

Hello Guys,

I trying to monitor the UPS using snmp but there are some missing mibs not working I don't know why ? can anyone support on this please

Sample MIBs

.1.3.6.1.4.1.318.1.1.1.2.2.4.0

1.3.6.1.4.1.318.1.1.1.3.2.1.0

1.3.6.1.4.1.318.1.1.1.4.2.2.0

 

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

Thanks a lot Gavan this will do the trick wink

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:16 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:16 AM

Any Help please it's a little bit urgent cry

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:16 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:16 AM

Hi Hasham,

Can you give us more detail on what your are trying to do?

The numbers your listed above are OIDs not MIBs, if you are looking for the correct MIB for the UPS then see below:

https://www.apc.com/shop/za/en/products/PowerNet-MIB-v4-3-2/P-SFPMIB432

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:15 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:15 AM

Hello Gavan,

I will try to be more specific. I'm trying to monitor the UPS using centralized monitoring solution, one of the items I want to monitor is 1.3.6.1.4.1.318.1.1.1.2.2.4 (upsAdvBatteryReplaceIndicator)

when I use snmpwalk to get the return of this OID I got below error message

No such object available on this agent at this OID 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:15 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:15 AM

Hi Hasham,

Not every OID in the MIB is applicable to every UPS.

If you provide me with a full SNMPWalk I can have a look, there may be an alternative that suits you UPS.

-Gavn

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:15 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:05 AM . Last Modified: ‎2024-03-08 03:15 AM

Hi Gavan

I used

snmpwalk -v2c -c public ups_ip 1.3.6.1.4.1.318.1.1.1.2.2.4

SNMPv2-AMI::enterprises.318.1.1.1.2.2.4 = No Such Object available on this agent at this OID

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

Hi Hesham,

You could use:

.1.3.6.1.4.1.318.1.1.1.2.1.1

The status of the UPS batteries.

A batteryLow(3) value indicates the UPS will be unable to sustain the current load, and its services will be lost if power is not restored. A batteryInFaultCondition(4)value indicates that a battery installed has an internal error condition."

INTEGER { unknown ( 1 ) , batteryNormal ( 2 ) , batteryLow ( 3 ) , batteryInFaultCondition ( 4 ) }

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

Hello Gavan,

Thanks a lot for you support, and please bear with me one last question, I need to monitor the operation mode, I mean I need to be alerted when the power cut off and the UPS starts to use the batteries

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

0 Likes
0
2714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

Hi Hesham,

There's probably few ways to do it but I would recommend monitoring:

.1.3.6.1.4.1.318.1.1.1.2.2.1 - upsAdvBatteryCapacity

And then set an alert if the number decreases by more than x% or goes below 95% (depending on your situation)

Or you could monitor:

.1.3.6.1.4.1.318.1.1.1.3.2.4 - upsAdvInputFrequency

If the input frequency is 0hz then there is no power coming to the UPS.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

0 Likes
0
2715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:06 AM . Last Modified: ‎2024-03-08 03:15 AM

Thanks a lot Gavan this will do the trick wink

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore