Can not return from the bypass mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Can not return from the bypass mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

0 Likes
3
1891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

Can not return from the bypass mode

After replacing all 4 batteries in Symmetra LX, we found out that

1) a red light blinks on one of IM,

2) a fan does not rotate at a full speed in one power module. 

We tried to resolve the situation and

1) removed the fault PM

2) replaced the fault IM with RIM when in Maintenance Bypass mode.

Of course, we got the UPS turned off.

After that, we can not return from the bypass mode (due to overload or fault).

Attached are files with dumps and logs.

Please, help.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

0 Likes
0
1891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

Hi David,

1) the system is not in  Maintenance Bypass.

2) Please, find attached pictures with status menu in rar files as you asked/

Best,

Igor

See Answer In Context

Attachments
RIM.rar
MIM.rar
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

0 Likes
0
1891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

Hello Igor, apologies for the delayed response on this. Typically when you have any kind of an issue with a Symmetra you should be contacting tech support before removing any questionable parts. The reason being is that the faults generated could be the result of something else in the system.

The logs that you provided show a redundant IM fault. The type of fault that it shows could actually be related to the main IM, though. 

Is the system still in Maintenance Bypass? If so, could you capture the readings from the "Status" menu on the display? Please do this with the main IM installed. Once you have done that, disconnect the main IM and let the redundant IM take control. Then capture the same data again. You can attach those logs here or email them to me directly to look at. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

Hi David,

thanks for your reply.

We disconnected and then connected back all system modules several times in different succession and have now a quite new situation.

The system is not in the bypass module but is functioning in a very strange way (see an attached zubbix report screenshot on the runtime on batteries).

There are several new errors in the log files we never had before the batteries replacing (e.g., An internal communication bus fault exists).

Please, find several files attached.

Best,

Igor

Best,

Igor

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

0 Likes
0
1892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:18 PM . Last Modified: ‎2024-03-06 11:14 PM

Hi David,

1) the system is not in  Maintenance Bypass.

2) Please, find attached pictures with status menu in rar files as you asked/

Best,

Igor

Attachments
RIM.rar
MIM.rar
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now