Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
Calculate expected PDU per rack
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2510:18 PM. Last Modified: 2024-03-1904:25 AM
Calculate expected PDU per rack
Hello - I have been looking for some guidance on rack design with regard to power usage. I have been asked to design our rack layout in terms of equipment placement and power consumption for each PDU.
We have both AP8861 20A (for servers) and AP8941 30A (for network equipment) PDU's and I am trying to calculate how much load the equipment in each rack will use, I can then plan where everything can go. We will have 2 PDUs per rack and use 3 phase power.
I used the calculation W/V=A - using the Wattage rating from the device documentation, 208 Volts to get Amps. This give me a higher number than i expected (i figured it would be an average, i understand it is not the max or min)
Am I calculating this incorrectly? Any guidance to documentation or help would be great!
I found the below info which looks to be along the correct lines:
This article will outline how phase current ratings and load calculations are determined as well as how load calculations are reached. AP8868 will be used as an example.
Resolution
In regards to the AP8868, each bank references two phases:
Bank 1 - Phase 1 and 2 Bank 2 - Phase 2 and 3 Bank 3 - Phase 1 and 3
AP8868 is one of the few units where the capacity is limited by the output circuit breakers and not the input cord/plug rating. The breaker on each bank is rated for 20A (de-rated to 16A per UL). Bank 1 draws current from phases 1 and 2 simultaneously. Bank 2 draws current from phases 2 and 3. This means that phase 2 is supplying current to both banks 1 and 2. However, like the phases, the banks are 120° out of phase. This means that part of the time that current is flowing one direction on bank 1, it is flowing the same direction on bank 2 and the two currents increase the draw from phase 2 to over 20A. However, at other times, when current is flowing one direction on bank 1, it is being returned on bank 2. This means that you can't just add the loads on the two banks to get the load on phase 2.
Here is another way to look at it. We are in essence supplying three 120V phases, but we are powering three 208V loads. If the loads are 16A, the total power consumed is (3 banks) x (208 Volts) x (16 Amps) = 9984 Watts. The current on the input must then be (20A x 208v x 3 banks)/(three phases x 120 Volts) = 34.6 Amps. This is how the total current per phase is determined but then please note the de-rating of values, per UL, which is 9984W.
Now that we know the load ratings, let's look at how to calculate the total power output.
For a single phase Rack PDU, Total Power = (Total Current) x (208V)
For a three phase Rack PDU, Total Power = (Total Three Phase Current) x (208V) x [sqrt(3)]
For a PDU like AP8868 with 3 banks, we'd use the single phase calculation for each of the three banks and then add them together to get the "Total Three Phase Current." The input of the Rack PDU is actually limited by the internal circuit breakers.