Bypass not in range; either frequency or voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Bypass not in range; either frequency or voltage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

0 Likes
4
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

Bypass not in range; either frequency or voltage

This error message comes and goes throughout the week. New to this, where should i begin to look for troubleshooting. The error will normally clear within 10 seconds.

Thanks,

MTB

Attachments
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

1 Like
0
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

Hi Matthew,

I received the logs. I can see this error is happening seemingly random. And when it does happen, it is only for 10-20 seconds usually. Unfortunately, only one instance in the event logs matches up with as far as the data log goes back. I don't see anything obvious in the data log causing it - voltage/frequency values around the event time in the log look normal - so it may be just too quick for the data log considering how that works.

This is one of those things that you could research if the times it happens via the event log, if any other devices, UPSs, etc also show alerts. My expertise is mostly with single phase UPSs but typically, we check to see if there is anything happening upstream or on the same circuit. A UPS of this size I would expect to be on a dedicated feed but I am not 100% how it would be set up. You would look to see if there is something feeding this that could cause a problem with voltage or frequency. If you have an in-house electrician or facilities person, this may be something they can check into. You can also consider emailing/contacting APC 3 phase support directly via email or phone for any further input.

Since it is happening for such short, random bursts, you could also considering configuring email delays for this event so you don't get email unless the event lasts for more than 20 seconds. I think the older Network Management Card firmware you have does not support that but if we verify it is an AP9617/18/19 we can upgrade it to support that capability. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

0 Likes
0
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

Hi Matthew,

From the screenshots, it looks like you have a 3 phase Smart-UPS VT product.

This error in general no matter the UPS, usually means that if the UPS has to go to bypass operation, the voltage and/or frequency is out of range. Depending on your settings, if it is out of range and UPS needs to go to bypass (due to overload, fault, etc), it won't be able to (may drop load) or would just go to bypass anyway and feed your equipment this voltage and/or frequency. This FAQ has a more comprehensive overview of what it means specific to your UPS model -> http://www.apc.com/us/en/faqs/FA173909

I would start by checking the event and data logs on your UPS Network Management Card. From the screenshot, it looks like you have an older firmware. (Check under Help->About System for AOS and app versions.) I don't think upgrading the firmware will do anything about this alarm but in newer firmwares, you may see better detailed logging. We can do this a little more longer term if you want to confirm what version you have now. We can then get you instructions/firmware files, if available.

You can check the event log for the timing of the events/alarms and see if the data log recorded anything for voltage/frequency that appears out of range. It may be occurring too quickly though to see a smoking gun in the data log though.

You can investigate if there is any electrical work being done on the input to this UPS as well after considering what the FAQ says. 

Hope this helps get you started. If you would like to post the logs for our review, you can extract data.txt and event.txt and share here. Instructions here -> http://www.apc.com/us/en/faqs/FA156131

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

0 Likes
0
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

Is this private between just us; or can everybody see my attachments?

MTB

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

0 Likes
0
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

Hi Matthew - this is public and attachments will be too. You can remove any sensitive info - IP address, names, etc and attach. Alternatively, you can email the files to a Box folder I have so only I'll see them: SUVT___.kmy6d93vwpoeylfv@u.box.com 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

1 Like
0
2112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:49 AM . Last Modified: ‎2024-03-19 01:50 AM

Hi Matthew,

I received the logs. I can see this error is happening seemingly random. And when it does happen, it is only for 10-20 seconds usually. Unfortunately, only one instance in the event logs matches up with as far as the data log goes back. I don't see anything obvious in the data log causing it - voltage/frequency values around the event time in the log look normal - so it may be just too quick for the data log considering how that works.

This is one of those things that you could research if the times it happens via the event log, if any other devices, UPSs, etc also show alerts. My expertise is mostly with single phase UPSs but typically, we check to see if there is anything happening upstream or on the same circuit. A UPS of this size I would expect to be on a dedicated feed but I am not 100% how it would be set up. You would look to see if there is something feeding this that could cause a problem with voltage or frequency. If you have an in-house electrician or facilities person, this may be something they can check into. You can also consider emailing/contacting APC 3 phase support directly via email or phone for any further input.

Since it is happening for such short, random bursts, you could also considering configuring email delays for this event so you don't get email unless the event lasts for more than 20 seconds. I think the older Network Management Card firmware you have does not support that but if we verify it is an AP9617/18/19 we can upgrade it to support that capability. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of