Bricked AP9631

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Bricked AP9631
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
avidrissman
avidrissman
Cadet

Posted: ‎2023-01-28 11:08 AM

0 Likes
1
1007
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-28 11:08 AM

Bricked AP9631

I bought a used APC SMT750 and a used AP9631. The AP9631 came with firmware 6.5.0, and I wanted to update it to the latest.

 

The latest is SFSUMX708, which explicitly lists “SmartUPS” and “AP9631”. So I downloaded it and ran it on my Windows VM.

 

What resulted was a failure:

 

[01/28/2023 13:36:15] Unable to update device 192.168.1.9 with Boot Monitor, stopping all further processing of this device!
[01/28/2023 13:36:15] Uploading firmware file 1 of 3: Boot Monitor to 192.168.1.9, please wait...
[01/28/2023 13:36:15] Firmware distribution does not match target device platform; this could be due to a corrupt distribution.
[01/28/2023 13:36:14] Downloading and verifying configuration file from 192.168.1.9, please wait.
[01/28/2023 13:21:291 NMC Firmware Update Utility v1.0.4 initialized.

 

The web interface started vending “The Application Was Not Able to Load ... Please login to the device via telnet for more details.” So I telnet-ed in:

 

apc>system
E000: Success
Host Name Sync: Disabled
Name: apc06C7FB
Contact: Unknown
Location: Unknown
Message:
DateTime: 04/09/2018:00:00:57
User: apc
Up Time: 0 Days 0 Hours 0 Minutes
Stat: P+ N4+ N6+ A-
Bootmon: Invalid Module Header!
AOS: Invalid Module Header!
App: Invalid Module Header!

 

So everything installed is toast. I was able to ftp in, so that’s still working:

 

ftp> ls
229 Entering Extended Passive Mode (|||53298|).
150 File status okay; about to open data connection.
--wx-wx-wx 1 admin admin 3055104 Jun 9 2017 apc_hw05_aos_650.bin
drwxrwxrwx 1 admin admin 0 Apr 9 0:00 db/
drwxrwxrwx 1 admin admin 0 Apr 9 0:00 ssl/
drwxrwxrwx 1 admin admin 0 Apr 9 0:00 ssh/
drwxrwxrwx 1 admin admin 0 Apr 9 0:00 logs/
drwxrwxrwx 1 admin admin 0 Apr 9 0:00 sec/
drwxrwxrwx 1 admin admin 0 Apr 9 0:00 dbg/
drwxrwxrwx 1 admin admin 0 Apr 9 0:00 fwl/
drwxrwxrwx 1 admin admin 0 Apr 9 0:00 email/

 

but I’m kinda wary now.

 

I can’t find something that matches my situation. Should I try to push this version of the firmware via FTP? Is there a better version or release to try?

 

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
avidrissman
avidrissman
Cadet

Posted: ‎2023-01-28 01:37 PM

0 Likes
0
998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-28 01:37 PM

Upon recommendation I used FTP to push the files, and it worked.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore