Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84245members
353345posts

Breaker reset on modular power unit

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
167

Breaker reset on modular power unit

This question was originally posted by James on APC forums on 3/8/2015


I have breakers that have 3 poles connected with 'handle ties'.  From what i gathered, this is safety mechanism for 3 wires sharing same neutral. No issue with that, but when a single leg trips due to device issue that backfeeds to the breaker, my question is, can I remove the handle tie to reset only that leg?  It appears the handle tie is removable and used for codes where needed.  I dont think it would be any code violation to remove it to reset the breaker, but I can not find any information on this.  Has anyone here had this experience?  I really do not want to reset all 3 phases as other devices do not need the added disruption of power off, then on.

this is on pdpm277 with breaker pdm3520, 3 phase, 5 wire breaker.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
167

Re: Breaker reset on modular power unit

This reply was originally posted by Angela on APC forums on 3/9/2015


Hello,

I checked with our 3 phase power team for help on this. Here is what they told me:

The installation of the handle ties are based on the load type (single or 3 phase & voltage).
This is regulated by the NEC.
IE: If the load is 120V single phase, then no handle tie is required since only a single pole breaker is needed for this type of load. If load is 208V or 277V single phase, then a 2 pole breaker is needed and therefore on a 3 pole breaker module, you would need a handle tie on 2 of the 3 breakers. If load is 208V 3 phase, then a handle tie would be needed across all 3 breakers.
The NEC Code requires that a circuit breaker providing power to any given load needs to open all current carrying conductors for that load at the same time during a fault.
So, if you are resetting a single phase load ( 120V or 277 ) then yes, you can reset the individual breaker, otherwise, no.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
168

Re: Breaker reset on modular power unit

This reply was originally posted by Angela on APC forums on 3/9/2015


Hello,

I checked with our 3 phase power team for help on this. Here is what they told me:

The installation of the handle ties are based on the load type (single or 3 phase & voltage).
This is regulated by the NEC.
IE: If the load is 120V single phase, then no handle tie is required since only a single pole breaker is needed for this type of load. If load is 208V or 277V single phase, then a 2 pole breaker is needed and therefore on a 3 pole breaker module, you would need a handle tie on 2 of the 3 breakers. If load is 208V 3 phase, then a handle tie would be needed across all 3 breakers.
The NEC Code requires that a circuit breaker providing power to any given load needs to open all current carrying conductors for that load at the same time during a fault.
So, if you are resetting a single phase load ( 120V or 277 ) then yes, you can reset the individual breaker, otherwise, no.