7902 firmware upgrade problems
  • 7902 firmware upgrade problems
Posted: ‎2021-07-01 07:03 AM . Last Modified: ‎2024-03-04 11:05 PM
1933
I upgraded four of our 7901 PDUs to v3.7.4 and for two of them, all of the data under the first menu choice "Device Manager" are missing.
  • ap7902
  • firmware
  • upgrade
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander
Ok. You have gibberish for the application string, and the app is not running properly (the "A-") in the Stat: section.
What is a little confusing is that it says it has been up for 15+ days, yet you said you just upgraded it? I would suggest re-running the upgrade utility and see if it clears things up.
Terry_Kennedy_apc
Commander
Right after you log in, do you see the bolded text below:
American Power Conversion Network Management Card AOS v3.7.4
(c) Copyright 2009 All Rights Reserved Rack PDU APP v3.7.4
Switched Rack PDU: Communication Established
If not, can you post what you do see there?
Edit - for some reason, although I see bold text in the preview, it doesn't show up in the post. The parts I am talking about are "Rack PDU APP v3.7.4" and "Switched Rack PDU: Communication Established".
Here is the output of one of the units that is having problems
BAD UNIT
(c) Copyright 2009 All Rights Reserved F~PW~~~~~~~~~V~~F~;V~uQ;F~uL~F~F~~V~~F~~F~~V~~F~3~ v~.~.V.~
Name : SWPL-R01PDU02 Date : 03/06/2015
Contact : SW-Cloud0IT@steelwedge.com Time : 14:12:03
Up Time : 15 Days 18 Hours 33 Minutes Stat : P+ N+ A-
------- Control Console -------------------------------------------------------
1- Device Manager
2- Network
3- System
4- Logout
- Main Menu, - Refresh
> 1
------- Device Manager --------------------------------------------------------
- Back, - Refresh
Terry_Kennedy_apc
Commander