Currently I have a Smart-UPS X 3000 with 43% load. I'm looking to buy another one for a system with about the same load. The difference is this 2nd site has a generator. The generator is a very large 50kw industrial type. I'm not sure the exact brand or model yet.
Should I go with another Smart-UPS X 3000 or look at the Smart-Ups On-Line models instead? Should I go with another 3000VA based on the above load or jump up to a 5000? I might install a couple more servers.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:04 AM . Last Modified: 2024-03-13 01:50 AM
The Output Power Capacity is lower wattage on the Online UPS so that's why I was thinking I may need to upgrade to a 5000.
Smart-UPS RT 3000VA: 2100 Watts / 3000 VA
Smart-UPS 3000VA RM 2U LCD 120V: 2700 Watts / 3000 VA
Even though they are both 3000va, will the load be higher on the RT ? My concern is if I add a couple more servers, the load might be higher than recommended. What do you think?
Message was edited by: Kurt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:04 AM . Last Modified: 2024-03-13 01:50 AM
A 43 % load is pretty low so i would say 3kva is acceptable... The smart ups online UPS are generally better with generators, however as long as they are properly sized/maintained etc, it may not be necessary. This line also offers no transfer time and a bypass functionality which may or may not be a feature you want or need.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:04 AM . Last Modified: 2024-03-13 01:50 AM
The Output Power Capacity is lower wattage on the Online UPS so that's why I was thinking I may need to upgrade to a 5000.
Smart-UPS RT 3000VA: 2100 Watts / 3000 VA
Smart-UPS 3000VA RM 2U LCD 120V: 2700 Watts / 3000 VA
Even though they are both 3000va, will the load be higher on the RT ? My concern is if I add a couple more servers, the load might be higher than recommended. What do you think?