Available runtime has been exceeded which causes server to reboot

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Available runtime has been exceeded which causes server to reboot
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

0 Likes
3
1438
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:41 PM

Available runtime has been exceeded which causes server to reboot

Hi all,

PCNS 4.1.0
AOS  3.7.3
SUMX 3.7.2

2 x Smart-UPS RT 3000 XL each with AP9618 NMC

PCNS installed on 4 Windows 2012 R2 servers (in redundant configuration).  VM/SCVMM is not used. 3 servers are configured to shutdown when 'UPS On Battery', the 4th when 'Runtime exceeded' with a delay of 120 seconds.

Low battery on both is configured to 2 minutes and Shutdown delay is 20 seconds on each. Runtime remaining is 22 & 25 minutes on the UPS'.

Everytime I reboot a server, a 'Available runtime has been exceeded' event is logged. This causes the server with the Runtime exceeded shutown event to fire.  I have removed it from the node, but still keep getting the runtime has been exceeded error.  Event log attached.

Is there any idea what to do to prevent such behavior?

Tony

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
1438
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:40 PM

Hi,

This issue is discussed in the User's Guide on page 34 and in PCNS help files.

Below is from the User's Guide:

Available runtime has been exceeded

For both conditions below, the “total shutdown time” includes the following durations:

  • Shutdown command file duration
  •  Built-in duration of 2 minutes (this consists of a 10 second OS shutdown duration and a 60 second OS shutdown duration; rounded up)

This event occurs with either of the following conditions:

Condition 1. When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Resolution: Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.

Condition 2. When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

Resolution:

1. Remove some equipment from the UPS to increase the available runtime.

2. Decrease the shutdown duration time for the UPS On Battery event.

3. Decrease the command file execution time using the Shutdown Settings screen. This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.

From reading your post I suggest increasing the low battery duration to 5 minutes. That should resolve the issue unless you have a delay set up that is not mentioned in the post. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
1439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:51 AM . Last Modified: ‎2024-02-14 10:40 PM

Hi,

This issue is discussed in the User's Guide on page 34 and in PCNS help files.

Below is from the User's Guide:

Available runtime has been exceeded

For both conditions below, the “total shutdown time” includes the following durations:

  • Shutdown command file duration
  •  Built-in duration of 2 minutes (this consists of a 10 second OS shutdown duration and a 60 second OS shutdown duration; rounded up)

This event occurs with either of the following conditions:

Condition 1. When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Resolution: Increase the Low Battery Duration value on the NMC using Configure - Shutdown or decrease the shutdown durations being used by PowerChute.

Condition 2. When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

Resolution:

1. Remove some equipment from the UPS to increase the available runtime.

2. Decrease the shutdown duration time for the UPS On Battery event.

3. Decrease the command file execution time using the Shutdown Settings screen. This event is logged and event actions are carried out even if it occurs on a single UPS in a Redundant or Parallel UPS configuration.

From reading your post I suggest increasing the low battery duration to 5 minutes. That should resolve the issue unless you have a delay set up that is not mentioned in the post. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
1438
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

Thanks Bill - have made the changes as above.

Can I ask a question about redundant mode?

If we have a power outage the UPS's take over.  In redundant mode, UPS1 runs takes all the load and runs until the battery runs out and then UPS2 takes over the load.  So I should have about 40 minutes runtime given the above figures (22 + 25), is this a correct overview?

Cheers
Tony

Reply

Link copied. Please paste this link to share this article on your social media post.

roger_apc
Ensign roger_apc
Ensign

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

0 Likes
0
1438
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:52 AM . Last Modified: ‎2024-02-14 10:40 PM

Hi Tony,

If the servers are dual corded, I would connect one cord to each UPS.  In normal operation, the load will be shared between the UPS units.  In this configuration, if either UPS were to fail, the servers would still be powered.  Automatic shutdown becomes a bit more complicated.  You would need to start your shutdown process when the UPS with the shorter runtime is about to fold.  However, this would have the side benefit of providing a bit of a pad against an extended shutdown period.

 

In our enterprise, we use rack mounted ATS units for any device that is single corded.

 

Cheers, 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of