Automatic Orderly Shutdown using PowerChute

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Automatic Orderly Shutdown using PowerChute
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:52 AM

0 Likes
7
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:52 AM

Automatic Orderly Shutdown using PowerChute

I have successfully installed the PowerChute Network Shutdown utility to a RHEL 4 box and a Windows 2k3 box both connected to an APC UPS. I sent a test shutdown command to the UPS and both of the boxes shutdown in an orderly fashion. My question is: is there a way to shutdown the servers in a particular order rather then the servers shutting down simultaneously?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

Excellent! It's working like a charm now. Thanks a lot for the help annwang and winna! I would also like to add as an FYI to anyone that finds this thread in a search that to access the Linux version of the PowerChute Network Shutdown utility you have to go to 127.0.0.1:3052 rather than 127.0.0.1:6547 on Windows.

Message was edited by: theblang

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

you can go to the configure events screen in powerchute network shutdown and configure the on battery event. for example, you can tell one server to shutdown after the UPS on battery event has lasted for 5 minutes and then the other server to shutdown after its lasted for 10. of course you want to check your total runtime and change your values appropriately. furthermore, the on battery event goes by seconds rather than minutes so you'd have to convert it to seconds ๐Ÿ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

In your case, you will need to uncheck "Turn off the UPS after the shutdown finishes. " on the first shutdown server. Otherwise, this server will signal the UPS to turn off after the shutdown finished. Then the NMC will signal to gracefully shutdown all of your servers (with PCNS installed) before the UPS turn off.

To do this, open PCNS UI on the first server, navigate to "Configure Shutdown" on the left, you will see this configuration. If you have more than 2 servers, please only keep this configuration enabled on the last shutdown server.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

Thanks a lot for the response winna. I actually just got finished testing that method. The problem I am now running into is that when one server shuts down (of the two on the UPS) they both shut down. My test results were as follows:

Test 1: I used the 127.0.0.1:port webapp on the Win2k3 box to set the On Battery event to 240 seconds, while setting the On Battery event on the Linux box to 120 seconds. I unplugged the UPS. Actual results were both boxes shutting down at approx. 120 seconds.

Test 2: I changed the Win2k3 box to 60 seconds while leaving the Linux boxs at 120 seconds. Actual results were both boxes shutting down at approx. 60 seconds.

So it seems that when one box issues a shutdown it causes all the boxes to shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

yeah, make sure you check the setting that Ann has mentioned. you definitely can stagger the shutdown on these machines.

as Ann mentioned, you only want to tell the last server to shutdown the UPS so you need to uncheck that checkbox that says 'turn the UPS off after this server shuts down' or something like that. only have it on the second or last server to shutdown.

let us know how that works out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

Another small issue. I have checked shutdown the UPS on the last server to go down but the UPS stays up.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

If you check the help file within PCNS, about half way down you'll see a timeline that shows the shutdown sequence. It will take a few minutes for that UPS shut down to initiate. Also keep in mind, if you plug the UPS back into the wall or provide power back to the UPS, it's only going to go off for a split second -> sense good input power -> and turn back on. Thus, cycling power to you equipment, which is how servers are rebooted.

You can conifigure if you want the UPS to stay off under the Powerchute option in the Network Management Card interface. It's default set to "Reboot online return" .. you can set it to "stay off".

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 08:18 PM . Last Modified: โ€Ž2024-03-15 02:51 AM

Excellent! It's working like a charm now. Thanks a lot for the help annwang and winna! I would also like to add as an FYI to anyone that finds this thread in a search that to access the Linux version of the PowerChute Network Shutdown utility you have to go to 127.0.0.1:3052 rather than 127.0.0.1:6547 on Windows.

Message was edited by: theblang

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of