Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Apc1- 9619 interface card, not able to load web interface.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
However, when I try updating one device (let's call it apc1), I get the following error message on the web interface: "Error: The application was not able to load. You are attempting to access an APC device. There was a problem loading the application. Please login to the device via telnet for more details."
But interestingly, when i did the exact same procedure previously on another device (apc4), the update was successful, and i was able to access the web interface without any issues.
So what have i done wrong?
Any help troubleshooting this would be greatly appreciated!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-1106:51 AM
So it turns out that in order to update the UPS firmware, I needed the default username and password (apc), even though I had already provided the new user and password. I assume there's some sort of check hardcoded into the script.
Using Telnet, I was able to reset the password, run the firmware update again, and this time it completed successfully, with the web interface returning. It was a really simple solution to what I initially thought was a major mistake on my part.
Maybe next time, I won't panic so quickly. Thank you.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-1106:51 AM
So it turns out that in order to update the UPS firmware, I needed the default username and password (apc), even though I had already provided the new user and password. I assume there's some sort of check hardcoded into the script.
Using Telnet, I was able to reset the password, run the firmware update again, and this time it completed successfully, with the web interface returning. It was a really simple solution to what I initially thought was a major mistake on my part.
Maybe next time, I won't panic so quickly. Thank you.