Both of these devices use their own version of serial over ethernet, but I am not able to make them communicate. Anyone else have this setup or know what type of cabling I need?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:33 AM . Last Modified: 2024-03-12 02:58 AM
So for the newer SMT/SMX model UPSs and AP9630/31 UPS Network Management Cards, you need to connect a serial cable directly to the 2.5mm Tip Ring Sleeve connector (labeled "console") on the AP9630 UPS Network Management Card itself. I believe you could do it this way and it should work the same:
AP9630 2.5mm console jack connection->2.5mm to DB-9 940-0299 APC NMC2 configuration cable->Digi
How did you have the 1400 connected? You may need a different connection or adapter between the DB-9 end of the 940-0299 and the digi connection, depending how it was before.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:32 AM . Last Modified: 2024-03-12 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:32 AM . Last Modified: 2024-03-12 02:58 AM
Both of these devices use their own version of serial over ethernet, but I am not able to make them communicate. Anyone else have this setup or know what type of cabling I need?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:33 AM . Last Modified: 2024-03-12 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:33 AM . Last Modified: 2024-03-12 02:58 AM
The ups has the 9630 card, but I am hoping I can set the ip address of the apc9630 card via the serial port. This is planned for a fleetwide installation that needs to be able to set the ip via software (Linux servers). With our previous model, a 1400, we did that. I guess something has changed.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:33 AM . Last Modified: 2024-03-12 02:58 AM
So for the newer SMT/SMX model UPSs and AP9630/31 UPS Network Management Cards, you need to connect a serial cable directly to the 2.5mm Tip Ring Sleeve connector (labeled "console") on the AP9630 UPS Network Management Card itself. I believe you could do it this way and it should work the same:
AP9630 2.5mm console jack connection->2.5mm to DB-9 940-0299 APC NMC2 configuration cable->Digi
How did you have the 1400 connected? You may need a different connection or adapter between the DB-9 end of the 940-0299 and the digi connection, depending how it was before.