An input voltage or frequency problem prevents switching to bypass mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • An input voltage or frequency problem prevents switching to bypass mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
3
2828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

An input voltage or frequency problem prevents switching to bypass mode

Last night we had some external power failures (the provider was resolving an external issue) and the result is this log. Need some help with this log analysis:

1. What kind of external power can make prevent switching to bypass mode?
2. It is supposed to switch to bypass mode when the batteries are exhausted?

Thanks for any help

PD: It is a Symmetra LX 16000

11/30/2010 10:39:25 UPS: A discharged battery condition no longer exists.
11/30/2010 10:38:35 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/30/2010 10:31:33 UPS: A low battery condition no longer exists.
11/30/2010 10:31:33 UPS: No longer on battery power.
11/30/2010 10:06:55 UPS: No longer in bypass.
11/30/2010 10:06:39 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
11/30/2010 10:06:36 UPS: In bypass in response to an overload.
11/30/2010 10:06:19 UPS: An input voltage or frequency problem prevents switching to bypass mode.
11/30/2010 10:06:17 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
11/30/2010 10:05:57 UPS: An input voltage or frequency problem prevents switching to bypass mode.
11/30/2010 10:05:56 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
11/30/2010 10:05:36 UPS: An input voltage or frequency problem prevents switching to bypass mode.
11/30/2010 10:05:35 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
11/30/2010 10:05:15 UPS: An input voltage or frequency problem prevents switching to bypass mode.
11/30/2010 10:05:14 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
11/30/2010 10:04:54 UPS: An input voltage or frequency problem prevents switching to bypass mode.
11/30/2010 09:39:45 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/30/2010 09:39:45 UPS: On battery power in response to an input power problem.
11/30/2010 09:38:52 UPS: A low battery condition no longer exists.
11/30/2010 08:57:03 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/30/2010 08:57:03 UPS: On battery power in response to an input power problem.
11/30/2010 08:56:19 UPS: A low battery condition no longer exists.
11/30/2010 08:38:51 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/30/2010 08:38:51 UPS: On battery power in response to an input power problem.
11/30/2010 08:38:08 UPS: A low battery condition no longer exists.
11/30/2010 08:19:26 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/30/2010 08:19:26 UPS: On battery power in response to an input power problem.
11/30/2010 08:18:39 UPS: A low battery condition no longer exists.
11/30/2010 06:52:42 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/30/2010 06:52:42 UPS: A discharged battery condition no longer exists.
11/30/2010 06:52:42 UPS: On battery power in response to an input power problem.
11/30/2010 06:52:20 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/30/2010 06:52:01 UPS: A low battery condition no longer exists.
11/30/2010 06:52:01 UPS: No longer on battery power.
11/30/2010 04:16:16 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
11/30/2010 04:16:16 UPS: A discharged battery condition no longer exists.
11/30/2010 04:16:16 UPS: On battery power in response to an input power problem.
11/30/2010 04:15:55 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
11/30/2010 04:15:35 UPS: No longer on battery power.
11/30/2010 01:06:12 UPS: On battery power in response to an input power problem.
11/30/2010 01:05:31 UPS: No longer on battery power.
11/29/2010 22:29:21 UPS: On battery power in response to an input power problem.
11/29/2010 22:28:39 UPS: A power module fault exists.

Message was edited by: Booga

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
0
2825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

Thank you very much, a clear explanation, your help is much appreciated.

Booga

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
0
2825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

Hi Booga,

The Symmetra has a few simple goals:
1) Keep the critical load powered
2) Provide conditioned power from the inverters whenever possible
3) Protect the load from receiving any poor quality power (from UPS or mains)

Therefore, at all times, the UPS evaluates the mains power to determine if it is acceptable to use in bypass mode. If the power modules are unable to provide inverter output either on-line or on-battery, the UPS will consider the option of bypass and will use it if the mains power is within an acceptable range.The power modules are able to remain on-line through a wide input range -- much wider than what the UPS would ever consider sending directly to the load.

By default, the UPS considers AC input acceptable if it is within -20% and +10% of the configured output voltage from the inverters. Frequency is also considered acceptable if it is within +/- 5Hz of the configured output frequency.

Therefore, your event log shows that at times, the input was inappropriate for bypass (outside specified range above) but the UPS was able to remain on inverter either on-line or on-battery.

If the power modules cannot operate due to exhausted battery or due to overload, the UPS will consider powering the load via bypass as long as the mains input is within the acceptable range.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

Thank you very much, a clear explanation, your help is much appreciated.

Booga

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

Hi Booga,

The Symmetra has a few simple goals:
1) Keep the critical load powered
2) Provide conditioned power from the inverters whenever possible
3) Protect the load from receiving any poor quality power (from UPS or mains)

Therefore, at all times, the UPS evaluates the mains power to determine if it is acceptable to use in bypass mode. If the power modules are unable to provide inverter output either on-line or on-battery, the UPS will consider the option of bypass and will use it if the mains power is within an acceptable range.The power modules are able to remain on-line through a wide input range -- much wider than what the UPS would ever consider sending directly to the load.

By default, the UPS considers AC input acceptable if it is within -20% and +10% of the configured output voltage from the inverters. Frequency is also considered acceptable if it is within +/- 5Hz of the configured output frequency.

Therefore, your event log shows that at times, the input was inappropriate for bypass (outside specified range above) but the UPS was able to remain on inverter either on-line or on-battery.

If the power modules cannot operate due to exhausted battery or due to overload, the UPS will consider powering the load via bypass as long as the mains input is within the acceptable range.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

0 Likes
0
2825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:19 AM . Last Modified: ‎2024-03-13 05:43 AM

So what shall i do if this message sill exist on the display?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore