An automatic voltage regulator (AVR) relay fault exists

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • An automatic voltage regulator (AVR) relay fault exists
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
7
22454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

An automatic voltage regulator (AVR) relay fault exists

Is this a call to replace the ups all together or is there something that can be done? 

Also I was wondering if what is in the log, that i will attach, is an issue with the power input or if the relay going out is causing these errors?

link to logs (the times and dates are off)

http://pastebin.com/gFyHb3Gu

thank you in advance for any help you may provide.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • avr
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
1
22440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

Hello,

What is the model of your UPS?  Usually, depending on your UPS, an AVR fault deems a replacement necessary.  The AVR is what is compensating for the low input voltages noted in your logs (which if true is an input/utility power problem).

If you can let us know the UPS model and serial number, we may be able to instruct you on a troubleshooting procedure to try and clear the fault.

Regards,

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

0 Likes
0
22440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

Jordan.

thanks for your suggestion. after following your troubleshooting steps it did finally reboot and for about 4-5 seconds i thought it would be ok but then it clicked and gave the p.06 error once again. I am reaching out to APC for warrenty as the unit is within its first two years of service. ( we installed it about 1 year ago. 

I will let you know what we determine.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
1
22441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

Hello,

What is the model of your UPS?  Usually, depending on your UPS, an AVR fault deems a replacement necessary.  The AVR is what is compensating for the low input voltages noted in your logs (which if true is an input/utility power problem).

If you can let us know the UPS model and serial number, we may be able to instruct you on a troubleshooting procedure to try and clear the fault.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

0 Likes
0
22440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:43 AM . Last Modified: ‎2024-02-14 10:50 PM

the model is a Smart-UPS X 1500 and the serial is AS1105223006

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

0 Likes
2
22441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

I would recommend what we call a braindead procedure:

1- Turn off the UPS

2- Unplug all load

3- Unplug the unit from utility

4- Disconnect all batteries

5- Hold down the power button for about 20 seconds

6- Reconnect the batteries, unit, and load

7- Bring the unit back online

If the fault clears, that is great, but if it does not, it is a true AVR fault and the UPS needs replacement.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

0 Likes
0
22441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

Jordan.

thanks for your suggestion. after following your troubleshooting steps it did finally reboot and for about 4-5 seconds i thought it would be ok but then it clicked and gave the p.06 error once again. I am reaching out to APC for warrenty as the unit is within its first two years of service. ( we installed it about 1 year ago. 

I will let you know what we determine.

Reply

Link copied. Please paste this link to share this article on your social media post.

federico.fiordoliva
federico.fiordoliva
Cadet

Posted: ‎2021-11-12 06:54 AM

In response to BillP
0 Likes
1
22184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-12 06:54 AM

Hi all,

i have the same ploblem, my ups is Samrt-UPS 1000 va.

Display report P.06 and red led is active.

Serial n. as2034360936

Model: SMC1000IC

 

The output was blocked.

 

 

Can you help me?

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

pgorman
Crewman pgorman
Crewman

Posted: ‎2022-09-01 05:57 AM

In response to federico.fiordoliva
0 Likes
0
19149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-01 05:57 AM

You are most certainly going to need a replacement unit VRM or what apc calls AVR is basically a chip that regulated and evens the voltage going thru it so the equipment on the other side is not damaged. It is going to be cheaper to get a new ups or warranty/ maintenance claim.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Abass_apc
Abass_apc
Cadet

Posted: ‎2024-03-07 11:39 PM

In response to BillP
0 Likes
0
10829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-07 11:39 PM

Smart-UPS 1000

s/n.  AS1044212049

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore