Amperage on the APC Smart-UPS RT 3000VA 120V
I cant find anywhere on the technical specs what the amperage is. Anyone know where I can find this information? I need to know what it is so we can make sure we have the right amount of power to supply these UPS's.
Thanks for any helpful information.
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-28 06:36 PM . Last Modified: 2024-03-15 03:54 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:36 PM . Last Modified: 2024-03-15 03:54 AM
Hello Jason,
The 120v RT 3000 UPSs both require a NEMA L5-30R recepticle (30 amp). You can see the input requirements on the UPS's product web page.
SURTA3000XL:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURTA3000XL
SURTA3000RMXL
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURTA3000RMXL
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 06:36 PM . Last Modified: 2024-03-15 03:54 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:36 PM . Last Modified: 2024-03-15 03:54 AM
Hello Jason,
The 120v RT 3000 UPSs both require a NEMA L5-30R recepticle (30 amp). You can see the input requirements on the UPS's product web page.
SURTA3000XL:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURTA3000XL
SURTA3000RMXL
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURTA3000RMXL