Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Adding a list of UPS to PCNS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Adding a list of UPS to PCNS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:30 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
10
2399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:30 AM . Last Modified: ‎2024-03-11 04:04 AM

Adding a list of UPS to PCNS

Hi everybody, Hi Bill,

what is the best practice to adding a lot of UPS without clicking the "Powerchute setup"?
can I import a CSV or something else? Script the NMC2 with powerchute clients?

The solution with INI Utility sounds great to me.

thanks in advance

best regards

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:03 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:03 AM

Hi,

PowerChute Network Shutdown is designed to react to signals sent from the network management card based on the status of the UPS. PowerChute Network Shutdown is not designed to be a monitoring or management tool. Its purpose is to shutdown the OS when the UPS is on battery, at low battery etc. A list of possible shutdown variables will be found in the PowerChute User's Guide under configurable events. 

If you need a tool to monitor and manage the UPS at multiple location through the network card you should look at EcoStruxure.  Another option is through a SNMP Agent. An example of an SNMP Agent is SolarWinds. 

Another note: you pointed to an old thread concerning the PowerChute VM. We do not support Advanced Redundant UPS configuration when PowerChute is running on a VM. Also, we list in the User's Guide that we tested PowerChute in Advanced Redundant UPS configuration with 16 UPS / NMCs. The User's Guide does states that you can add more to allow users to determine their own best practices. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:30 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:30 AM . Last Modified: ‎2024-03-11 04:04 AM

Hi,

Do you want to add UPS to the PCNS client or do you want to add PCNS clients to the UPS? 

In the pcnsconfig.ini there is a section that represents the UPS/s the PCNS client is registered with. See Schneider Electric FAQ FA159757

[NetworkManagementCard]
mode = single
IP_1 = 192.168.1.11
port = 80
protocol = http
enrolWithNMC = true
acceptCerts = false
IP_1_Outlet = 1
Note: you can only add 4 UPS to a single PCNS client unless you are configuring for Advanced Redundant UPS. 

To add PCNS clients to the NMC you can edit the NMC config.ini file. 

[PowerChute]
;   PowerChute Network Shutdown, provides reliable network based shutdown of 
;   multiple computer systems to enhance the manageability of APC UPSs in 
;   datacenter environments. To add a client server, simply list the IP as such:
;   CurrentPCNSClientIP0=192.168.0.1
;   To associate an outlet group with a client where the groups are numbered 
;   0 to n with 0 being the main outlet group (if present on UPS)
;   PCNSClientIPGroup= 0
;   To remove a specific client, list the client using the keyword:
;   RemovePCNSClientIP=192.168.0.2
;   To remove all configured clients, use the keyword, value pair:
;   RemoveALLPCNSClientIP=yes
;   To change the Authentication Phrase, use the AuthPhrase keyword 
;   i.e., AuthPhrase=apc auth passphrase
OnBatteryShutdownBehavior=Reboot On Line Return
PCNSUserName=apc
CurrentPCNSClientIP1=192.168.1.10
PCNSClientIPGroup1=1
OutletGroup1PCNSShutdownControl=enabled
OutletGroup2PCNSShutdownControl=enabled
OutletGroup3PCNSShutdownControl=enabled
OutletGroup1PCNSOffDelayControl=enabled
OutletGroup2PCNSOffDelayControl=enabled
OutletGroup3PCNSOffDelayControl=enabled
OnBatteryShutDownStatus=disabled
OnBatteryShutDownDelay=120
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

Hi Bill,

thanks for you answer, sorry for my late answer I was busy with other tasks.

first I tried to add all NMC to PCNS, the APCs were listed in the PCNS, but it wasn't pushed to the UPSs

Then I tried to edit the NMC Config, but in the config is the IP address, and if I want to reupload a NMC Config, I hoped that its possible to uploade only a few settings. The problem is, that if I create and upload a config with IP, every NMC get the same IP address, the 2nd way to upload a NMC config without the section IP address will overwrite it to blank, and the APC is lost.

I know I got very dumb questions.

Thanks a lot for helping me all the time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

Hi,

Do you want to add multiple PCNS clients to a NMC. If that is the case you would add the PCNS client IPs to a NMC config.ini and then push that file to the NMC. 

Schneider Electric FAQ FA156117 discusses mass configuration of NMC. I followed the steps to add just PowerChute client to the config.ini and the clients were added to the config.ini when I copied the PowerChute.ini to the NMC. I have attached the test PowerChute.ini file. 

NOTE: I had to change the name to PowerChute.txt to attach to this post. If you want to use the file you will need to change the extension to .ini

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

Hi Bill,

this worked perfectly thanks a lot, I updated all my NMCs.

But now I'm looking for a faster way to add all NMC(APCs) to the central PCNS, with editing the pcnsconfig.ini 

1. in this section:

IP_1 = 10.xx.xx.xxx
IP_2 = 10.xx.xx.xxx
IP_3 = 10.xx.xx.xxx
IP_4 = 10.xx.xx.xxx
IP_5 = 10.xx.xx.xxx
IP_6 = 10.xx.xx.xxx

and 2. section

[advanced_ups_setup_4]
setup_name = namexyz
ip_addresses = 10.xx.xx.xxx
ups_required_for_load = 1
shutdownCommandFileEnabled = false
shutdownCommandFileDuration = 0
shutdownOnLostRedundancy = false
turnOffUps = false
turnOffSOG = false
executeCommandFileAfterHostShutdown = false
shutdownCommandFileDelay = 0
hostlist = xxxxxxxxxxxxxxxxxxxx&0
force_VApp_shutdown = false
enable_guest_vm_migration = true
guest_vm_migration_duration = 270
enable_custom_target_vm_migration = false
custom_target_hosts =
enable_guest_vm_shutdown = true
guest_vm_shutdown_duration = 270
enable_guest_vm_startup = true
guest_vm_startup_duration = 360
enable_VApp_shutdown = false
VApp_shutdown_duration = 120
enable_VApp_startup = false
VApp_startup_duration = 120
vm_startup_delay_duration = 0
ShutdownVirtualHosts = false
shutdownPowerchuteServer = false


and then the entries are listed on the PCNS Webinterface on the left site with Error Accessing(see embedded screenshot), but then I have to do the Powerchute Setup again to enable the communication.

7zi5e%2FI62ggLF7yrXDx6FQ%3D%3D.png7zi5e%2FI62ggLF7yrXDx6FQ%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

Hi,

How I have done this in the past is to install PCNS on a system and configure for VMware and Advanced Redundant UPS through the web interface. Then on the secondary system I installed PCNS silently configuring for basic setup e.g. single UPS. When the silent install has completed I stop the PCNS service, copy the pcnsconfig.ini file from the original system to the secondary system, edit it as needed, and then restart PCNS. The secondary system is now configured for VMware with Advanced Redundant UPS.

NOTE: Advanced Redundant UPS configuration is not support when PCNS is running on a VM. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

perfect!

sorry for the dumb question, I put all my APC in the pcnsconfig.ini with IP = xx.xx.xx.xxx and IP_xx_Outlet

im totally a beginner in scripting and powershell, I want to script the advanced setup, I got all entries of my APCs in an excel sheet,

and I only want to count the number at[advanced_ups_setup] +1, and fill the setup_name and ip_adresses from the excel sheet....

[advanced_ups_setup_6]
setup_name = namexyz
ip_addresses = 10.xx.xx.xxx
ups_required_for_load = 1
shutdownCommandFileEnabled = false
shutdownCommandFileDuration = 0
shutdownOnLostRedundancy = false
turnOffUps = false
turnOffSOG = false
executeCommandFileAfterHostShutdown = false
shutdownCommandFileDelay = 0
hostlist = xxxxxxxxxxxxxxxxxxxx&0
force_VApp_shutdown = false
enable_guest_vm_migration = true
guest_vm_migration_duration = 270
enable_custom_target_vm_migration = false
custom_target_hosts =
enable_guest_vm_shutdown = true
guest_vm_shutdown_duration = 270
enable_guest_vm_startup = true
guest_vm_startup_duration = 360
enable_VApp_shutdown = false
VApp_shutdown_duration = 120
enable_VApp_startup = false
VApp_startup_duration = 120
vm_startup_delay_duration = 0
ShutdownVirtualHosts = false
shutdownPowerchuteServer = false

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

Nevermind got it already... but now I got the same problem, like my first request here...

if I put about 150 APCs to my central PCNS appliance it runs again with 100% CPU...

is there a best practice amount of APCs connected to a PCNS?

Thanks a lot

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

Hi,

What are you attempting to accomplish with this configuration? Also, are all of the UPS at the same location?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

0 Likes
0
2400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:04 AM

Hi Bill of course not, they are at different locations.

see my old post "http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/84347/pcns-..."

I thought this appliance should be a central management for all APCs with advanced config in all locations.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:03 AM

0 Likes
0
2401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:31 AM . Last Modified: ‎2024-03-11 04:03 AM

Hi,

PowerChute Network Shutdown is designed to react to signals sent from the network management card based on the status of the UPS. PowerChute Network Shutdown is not designed to be a monitoring or management tool. Its purpose is to shutdown the OS when the UPS is on battery, at low battery etc. A list of possible shutdown variables will be found in the PowerChute User's Guide under configurable events. 

If you need a tool to monitor and manage the UPS at multiple location through the network card you should look at EcoStruxure.  Another option is through a SNMP Agent. An example of an SNMP Agent is SolarWinds. 

Another note: you pointed to an old thread concerning the PowerChute VM. We do not support Advanced Redundant UPS configuration when PowerChute is running on a VM. Also, we list in the User's Guide that we tested PowerChute in Advanced Redundant UPS configuration with 16 UPS / NMCs. The User's Guide does states that you can add more to allow users to determine their own best practices. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore