Accuracy of APC Environmental Manager?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Accuracy of APC Environmental Manager?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
4
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

Accuracy of APC Environmental Manager?

Does APC have an accuracy rating for the ap9340? I am trying to use one as part of a Smart Home that I am configuring. This device will monitor the wine cellar, for humidity and temperature. The room is approximately 8 x 56. I am planning on using a TH probe at both ends, but will that be accurate enough for monitoring purposes? Help is appreciated. Thanks - BD

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • environment
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

You're welcome powerUP. If any other questions arise please don't hesitate to start another post.

Take it easy.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

Thanks for answering so quickly. I can finally get the ball rolling on this project. This accuracy should be fine for what we are doing, its more of a convenience/show project rather than a precision controlled environment. Netbotz are too expensive, even for this client!

Many thanks ~~

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

Sorry, I cut and pasted the info from a manual and the info is a little garbled.

AP9335T/TH
Temperature accuracy 3F (2C), from 32 to 104F (0 to 40C)
Humidity accuracy 4% RH, 20 to 90% RH, at 77F (25C), 8% RH, 30 to 80% RH,from 59 to 95ºF (15 to 30C)
Sensor operating temperature 14 to 159F (0 to 70C)

AP9520T/TH
Temperature Accuracy 1.8F (1.0C)
Temperature Drift 0.36F (0.2C)/over life of unit
Humidity Accuracy (AP9520TH) 3.0% RH @ 25C
Humidity Drift (AP9520TH) 1.0% RH/5 years

Hope this helps.

Message was edited by: KVM4Life

Message was edited by: KVM4Life

Message was edited by: KVM4Life

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

Hello,

The AP9340 can utilize two different sensors, the AP9335T/TH and the AP9520T/TH. These are not precision sensors, but are still pretty accurate. In regards to the size of the room, 8 x 56, it depends on how accurate you need the readings to be. If 1-2 isn't enough, you can daisychain multiple sensors off the AP9340. The AP9335TH is considered a "local" sensor, meaning it connects to the unit direct. The distance on the cable is about 6-8 feet. However, the AP9520TH can cascade off of the Alink port, which communicates over Cat5 cabling. You can connect a total of (8) AP9520TH's off of the unit. Perhaps you could set up 8 different zones?

You could also check out the Netbotz environmental products to see how accurate their devices are.

Here are the specs on the two sensors.

AP9335T/TH
Temperature accuracy ± 3ºF (± 2ºC), from 32 to 104ºF (0 to 40ºC)
Humidity accuracy ±4% RH, 20 to 90% RH, at 77ºF (25ºC), ±8% RH, 30 to 80% RH,from 59 to 95ºF (15 to 30ºC)
Sensor operating temperature 14 to 159ºF (?10 to 70ºC)

AP9520T/TH
Temperature Accuracy* ± 1.8° F (1.0°C)
Temperature Drift* ± 0.36°F (0.2°C)/over life of unit
Humidity Accuracy (AP9520TH) * ± 3.0% RH @ 25°C
Humidity Drift (AP9520TH) * ± 1.0% RH/5 years

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

You're welcome powerUP. If any other questions arise please don't hesitate to start another post.

Take it easy.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore