Accessing Network Management Card #AP9619

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Accessing Network Management Card #AP9619
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
5
1643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

Accessing Network Management Card #AP9619

Hello All-

We have a Network Management Card #AP9619 in our SymmetraF UPS. Card has activity lights and such but we cannot seem to access it over our LAN. Is there a way to reset the card to DHCP? I did see a little reset pin area on the back plate of the card but am not convinced it actually reset. The way I see it, if it reset to defaults it should puick up an IP address right away. I scoped my LAN with Orion Lan Surveyor, however and could not see it anywhere. FYI- I already found this KB article and seem to be at an impasse.

http://emea-en.apc.com/app/answers/detail/a_id/3061/~/how-do-you-make-a-network-management-card-comm...

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

"That just tells you Syracuse wasn't that Griffey Shoes good," Barkley retorted. There will probably be people Air Jordan Heels who agree with Barkley that only eight Big East teams belonged in the NCAA tournament Ken Griffey Shoes as a result of the conference's awful showing, but the truth is the league simply performed well below Air Max 24 7 expectations in single-elimination format. Based on their season-long body of work, it would have been very difficult to justify leaving Nike Air Yeezy out Connecticut, Villanova or Marquette, the teams that finished ninth, 10th and 11th in the Big East regular-season standings. Even Nike Dunk Heels though he had the more logical argument, Pitino didn't exactly help himself when he looked straight into the camera and guaranteed "Notre Dame will not lose" Sunday night against Florida State. The lesson here: Never pin your TV credibility to Notre Dame in the NCAA tournament and never argue with Barkley even when you're right.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

If the reset function isn't working the card probably has had a Static IP configured. I'm not sure what type a SymmetraF UPS is but the larger Symmetra systems allow you to serial into the NMC via the serial port using the 0024C or D cable. Do you have this cable? DO NOT TRY TO SERIAL IN WITH ANYTHING OTHER THAN THIS CABLE, YOU RISK A LOAD LOSS WITH A NORMAL SERIAL CABLE.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

upsguy-

Thanks for the reply- unfortunately we do not have the desigamated serial cable. And yes, I had heard stories of that problem before so I resisted the temptation of digging out a standard RS-232 cable. I thought that maybe you could shunt a pin or two together to reset it while under power than power down and remove the card and remove the shunt. I will pull the card again and look at the reset recess, maybe we didn't hit it correctly.

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

upsguy-

I just had a hair-brained idea...maybe connect the NM card to a small switch or better yet hook up a LAN crossover cable and check it with a laptop. Maybe a netstat or other command might show me what the IP of the card is. I suppose I could even use my laptop (with LAN surveyor on it) this way and let it discover what the IP of the card is... just a thought...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

Try to configure you nmc with the apc software ( APC device ip configuration wizard) linked with network cable to your nmc, and don't forget to configure the lan port of pc with the same range of ip address.
example if you need to configure the nmc with tcp/ip:192.168.1.4, the configuration tcp/ip of your pc port must be :192.168.1.10
if you want to make your own serial cable to communicate with the nmc through serial com,i can give you the pin configuration upon request.
NOTE: the reset button is not useful without the serial com and hyper terminal program.

Message was edited by: Elec

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

0 Likes
0
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:09 AM . Last Modified: ‎2024-03-19 01:07 AM

"That just tells you Syracuse wasn't that Griffey Shoes good," Barkley retorted. There will probably be people Air Jordan Heels who agree with Barkley that only eight Big East teams belonged in the NCAA tournament Ken Griffey Shoes as a result of the conference's awful showing, but the truth is the league simply performed well below Air Max 24 7 expectations in single-elimination format. Based on their season-long body of work, it would have been very difficult to justify leaving Nike Air Yeezy out Connecticut, Villanova or Marquette, the teams that finished ninth, 10th and 11th in the Big East regular-season standings. Even Nike Dunk Heels though he had the more logical argument, Pitino didn't exactly help himself when he looked straight into the camera and guaranteed "Notre Dame will not lose" Sunday night against Florida State. The lesson here: Never pin your TV credibility to Notre Dame in the NCAA tournament and never argue with Barkley even when you're right.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore