Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

AVR (boost/trim) differences between UPS models

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AVR (boost/trim) differences between UPS models
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
160
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
marting
marting
Contributor

Posted: ‎2023-06-04 12:35 PM

0 Likes
4
3818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-04 12:35 PM

AVR (boost/trim) differences between UPS models

Hi all,

 

We have various models of APC UPSes deployed at one of our sites and I'm seeing an interesting difference in the performance of the Automatic Voltage Regulation functionality between different line-interactive UPS models.

 

Last night - due to an increase in voltage from the utility, we had multiple UPSes kick into AVR mode (Event message: "UPS: Compensating for a high input voltage.").

 

While in this state:

  • On a Smart-UPS 750, the output voltage dropped to ~ 110 - 112.5V
  • On a Smart-UPS 3000 X, the output voltage stayed at 119.9 - 120V the whole time

 

Looking at the event logs on the UPSes, it doesn't look like either of them kicked over to battery so I'm assuming the AVR feature is trimming the voltage.

 

Question: both of these UPSes list AVR as a feature but the performance is significantly different.  Is there a way to tell from spec sheets, etc. what level of AVR exists on any given UPS model?

Labels
  • Labels:
  • Other Environmental Monitoring Products & Questions
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • Automatic Voltage Regulation
  • avr
  • boost
  • english
  • trim
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Teken
Champion

Posted: ‎2024-01-11 01:41 PM

0 Likes
0
3584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-11 01:41 PM

Generally speaking, the AVR is defined by upper and lower voltage limit defined under the Configuration -> Power Settings. The *Sensitivity* that is chosen from (Normal, Reduced, Low) will define when the UPS will transfer to battery power - I have appended a screen shot from the users manual.

 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

joc112
joc112
Explorer

Posted: ‎2026-03-05 04:08 PM

0 Likes
2
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-03-05 04:08 PM

Were you able to figure out why you saw these differences in AVR performance? Also, did that event message show up on your smartconnect.apc.com dashboard or are you monitoring differently?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-03-06 03:15 AM

In response to joc112
0 Likes
0
844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-03-06 03:15 AM

As stated in 2024 the AVR circuit is defined in the power settings where the user has a limited range to choose from.

 

Depending upon model and firmware in place the upper and lower voltage transfer range is defined by the Local Power Quality setting.

 

Some units have the option to define the output voltage from 110, 120, 125 VAC. If this specific option is present it would offer tighter output voltage.

 

Other factors that affect the output voltage is Green Mode if available to enable / disable.

 

Other important considerations as it relates to both AVR / Battery only voltage output are design topology, component tolerance, age of system, firmware, and user defined selections.

 

A double conversion topology UPS will almost always have a tighter AC output vs a Line Interactive system. 

 

Lastly, the AVR output is physically defined by the transformer and where it’s tapped on the windings to buck / boost.

 

Questions Ask . . . 👍 

Reply

Link copied. Please paste this link to share this article on your social media post.

marting
marting
Contributor

Posted: ‎2026-03-16 08:53 AM

In response to joc112
0 Likes
0
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-03-16 08:53 AM

I was not able to figure out why the UPSes were behaving differently.  They were both line-interactive (not double online conversion) models so - in theory - behavior should be similar.

 

I got the alerts via the DCE software, but the alerts should show up in the UPS log as well.

 

My understanding of the lower/upper voltage tolerance settings is that the UPS will actually kick over to battery if the voltage is outside the specified range; those settings are usually significantly off from the nominal/desired voltage.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore