ATS dropped power to all protected devices

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ATS dropped power to all protected devices
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
3
2197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

ATS dropped power to all protected devices

I have an AP7721 ATS.  Both inputs are fed from separate APC UPSes (SMX3000RML).

Yesterday there was a power surge that tripped the breaker for the UPSes.  Both UPSes reported that they were "on battery power in response to distorted input".

When the breaker was flipped back on, power to all devices (network switches) behind the ATS was dropped.

There's nothing quite like the feeling of running to the server room and seeing your core and access switches rebooting...

Servers connected to the UPSes (not through the ATS) did NOT lose power (they are fed through a different outlet group from the ATS).

How is this even possible?  Equipment backed by redundant UPSes and fed through an ATS should not loose power unless BOTH UPSes are faulty (in which case the servers should have gone down too).

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:49 PM

0 Likes
0
2197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:49 PM

There are some devices that you just can't please, no matter what. I have a piece of equipment (Meridian Audio) that will reboot from the UPS just changing taps (for voltage boost).

You might try asking your ISP for either a different piece of equipment, or adding the redundant power supply if the unit is dual-supply or RPS capable. If it is a piece of Cisco equipment, would you mind sharing the model number? I use a fair amount of Cisco gear and might be able to shed some light on issues with specific models, like bad caps in some Catalyst 3750's.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
0
2197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

The ATS relies on a very short time period between deselecting one input and selecting the other. Anything like old relays or other aged components can lead to a "make before break" transfer where both the A and B inputs are connected to the output. This can cause various problems including dropping the load, damaging the ATS relays, or even tripping one or both upstream breakers.

My (locally-developed) best practices are:

  • Make sure the ATS reports the inputs as "in sync". If not, move one source to a different phase until the ATS reports "in sync".
  • Make sure the ATS has the latest firmware. The firmware bundle includes a separate firmware file for the actual ATS controller. Observe the warnings in the knowlegebase article about disconnecting one source before updating.
  • Configure the ATS as non-reverting (preferred source none). This will eliminate non-essential transfers (transfers just for the sake of getting back to the preferred source after a switchover).
  • Configure the ATS with sensitivity low if possible to eliminate unnecessary transfers.
  • If connecting the ATS with one or both sources connected to the output of a UPS, configure the UPS with a delay when returning to AC power (going off battery). If using multiple UPSs, configure a reasonable difference (30 seconds or more) between the UPSs, so they don't both transfer at the same time.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:49 PM

0 Likes
0
2197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:49 PM

Yes, I'm aware that the ATS complies to power switching that is within the tolerance for most device PSUs (1/60th of a second).

The UPSes are less than 3 years old.  Everything on the ATS is brand new (purchased this year) network switches.  Cisco and HP.

The ATS was configured with a non-preferred source (it may not be right now, but it definitely was before).

In initial testing only the ISP supplied network device has issues when switching between sources (reboots no matter what if the input source is changed).  This continues to be the case when testing after the outage.

Since the outage I have changed sensitivity to low, and increased the allowable voltage range (now at medium - 12V).

I will look into changing the UPSes to resume AC power with different delays.  Thanks for that tip - I had not considered that before.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:49 PM

0 Likes
0
2198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:49 PM

There are some devices that you just can't please, no matter what. I have a piece of equipment (Meridian Audio) that will reboot from the UPS just changing taps (for voltage boost).

You might try asking your ISP for either a different piece of equipment, or adding the redundant power supply if the unit is dual-supply or RPS capable. If it is a piece of Cisco equipment, would you mind sharing the model number? I use a fair amount of Cisco gear and might be able to shed some light on issues with specific models, like bad caps in some Catalyst 3750's.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore