Hi everyone, I am new to the Schnieder Products and have recently purchased and installed an APDU10351SM for my current project. I have multiple device that I am intend to power off/on in the event that they can not be recover from other ways and need to full reset.
I can use web and ssh to login to the PDU
When using SSH to the device I can turn on/off a single outlet "dev outlet 1 1 off/on" however i can not turn multiple on/off "dev outlet 1 1-4 on/off"
Also, what is the OS? apc?
once I can do this from the CLI I am looking to create a on/off.py
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-17 05:35 PM
Though SSH you can use the oloff 1-4 to turn off outlets one though four. You can also group outlets in the web interface for devices that have more than one PSU then by turning on/off one of those outlets turns them all on or off in the group