Hi, we have an 2200 SMT connected directly to a 16amp breaker and had a power outage yesterday evening where the battery discharged completely.
Upon tending to the issue this morning and power coming back online we found the 16amp breaker had tripped.
We switched it back on and it tripped again and again.
We removed the 2200 UPS from the circuit and charged it elsewhere (without load). at this point we where able to introduce the UPS back onto the 16amp circuit and it has been fine since.
My question is, what is the maximum charging current of this UPS and should additional load be included in this figure if outlets are set to switch on immediately?
Surely it should spike anywhere near the maximum capacity of the 16amp circuit but this seems to be what is happening?
Many thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 05:16 AM . Last Modified: ‎2024-03-18 03:38 AM
In Australia the C19 cables are supplied fitted with a 15A plug (We do 10, 15 & 20). At worst a 2200VA UPS *should* draw < 10A fully loaded and charged (with a really bad power factor). My measurements seem to indicate they draw 50-80W on top of the actual load. Charging you can add an extra 2-300W on top, so another amp. You should *never* pop a 16A breaker. Is it a combined MCB/RCD by any chance?
Even a 3000VA UPS should sit within 15A fully loaded.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 05:16 AM . Last Modified: ‎2024-03-18 03:38 AM
Hi Martin,
The SMT2200 has an NEMA 5-20 input plug meaning that it is to be used with a 20 amp circuit. If the circuit breaker on the circuit is only rated for 16 amps, it could easily trip while the unit is charging, especially at higher loads.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 05:16 AM . Last Modified: ‎2024-03-18 03:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 05:16 AM . Last Modified: ‎2024-03-18 03:38 AM
Hi,
Many thanks for replying.
i'm in the UK and the UPS was supplied with a C19 power cable which i've just checked and has a 13 Amp fuse.
The correct model UPS is APC SMART UPS 2200VA RM LCD 230V (SMT2200RMI2U) - www.misco.co.uk
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 05:16 AM . Last Modified: ‎2024-03-18 03:38 AM
Hi Martin,
I apologize for the confusion. As far as I know, a 16A circuit should be adequate for that unit. However, at this point I would recommend calling in to our tech support line for further troubleshooting. This issue would be better solved over the phone.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 05:16 AM . Last Modified: ‎2024-03-18 03:38 AM
Hello Team,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 05:16 AM . Last Modified: ‎2024-03-18 03:38 AM
In Australia the C19 cables are supplied fitted with a 15A plug (We do 10, 15 & 20). At worst a 2200VA UPS *should* draw < 10A fully loaded and charged (with a really bad power factor). My measurements seem to indicate they draw 50-80W on top of the actual load. Charging you can add an extra 2-300W on top, so another amp. You should *never* pop a 16A breaker. Is it a combined MCB/RCD by any chance?
Even a 3000VA UPS should sit within 15A fully loaded.