APC UPS SU3000NET multi clicking noise

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC UPS SU3000NET multi clicking noise
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

0 Likes
4
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

APC UPS SU3000NET multi clicking noise

Hi pals,

My APC UPS su3000net is giving multiple clicking (all) relay noise with all the leds flashing according to the clicking noise of the relays. Any info on what could be the cause and how to remedy it. Pls help out and thnx.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

On the uC, pin 9 is the reset pin. Pin 7 is bit 2 of the 8 bit bus that generates the reference sine-wave on the DAC.

If pin 31 is 2.8V then I assume pin 40 is 2.8v (which is the primary +5V supply for the uC). Sounds like you have a power supply issue.

For giggles, check pin 12, 19 or 20 on U10 (which is the ADC0838 A/D converter), if you have less than 5V there then you have an obvious issue with the 5V logic supply. It could be the 5V reg, but more likely something is shorted (or very low impedance) on the 5V rail and pulling it down.

Make sure you are using an appropriate ground reference to make these measurements. The Tab on IC5 (the 5V Reg) is a good place to pick up a logic ground if you haven't got one already as are pins 4 & 9 on the D9 connector on the back panel.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

I'll answer here rather in the other thread. No. The Leds are driven from a shift register in the panel. The Relays are driven from dedicated outputs on the uC via transistor buffers. It sounds like the uC is going birko and flashing its output pins. An 8051 will do that when configured for external memory. Perhaps the uC has lost its mind. That one I can't help with. Is the fan turning on and off as well? I ask because on the SU series the fan control is on the same 8 bit port as the panel serial link.

Check pin 31 on the uC. It should be high (~5V). That's the external memory enable. Also check pin 9 to make sure it's not toggling (reset pin).

Grab a data sheet for a DIP40 80C52 uController and have a poke around.

Do a google search for E735Gschem.pdf. It's a different model, but it's an SU series and the schematic might help you out with your SU2200 repairs also.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

On , said:

I'll answer here rather in the other thread. No. The Leds are driven from a shift register in the panel. The Relays are driven from dedicated outputs on the uC via transistor buffers. It sounds like the uC is going birko and flashing its output pins. An 8051 will do that when configured for external memory. Perhaps the uC has lost its mind. That one I can't help with. Is the fan turning on and off as well? I ask because on the SU series the fan control is on the same 8 bit port as the panel serial link.

Check pin 31 on the uC. It should be high (~5V). That's the external memory enable. Also check pin 9 to make sure it's not toggling (reset pin).

Grab a data sheet for a DIP40 80C52 uController and have a poke around.

Do a google search for E735Gschem.pdf. It's a different model, but it's an SU series and the schematic might help you out with your SU2200 repairs also.

Yea the fan is running.

Please watch the attached video for a clearer info on the problem of the ups.

Thanks for the initial response.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

Good day, I've did a check on the system and here are my findings;

1. Pin 31 is giving 2.8v against the 5v,

2. Pins 9 & 7 being the reset pins are giving respective 1.8 and 1.9v and

3. The fan is receiving normal 24v even as the system is misbehaving.

Those are my findings, pls what do you think I should do next to get this system working.

Thanks once again.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

0 Likes
0
1231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:28 AM . Last Modified: ‎2024-03-18 01:29 AM

On the uC, pin 9 is the reset pin. Pin 7 is bit 2 of the 8 bit bus that generates the reference sine-wave on the DAC.

If pin 31 is 2.8V then I assume pin 40 is 2.8v (which is the primary +5V supply for the uC). Sounds like you have a power supply issue.

For giggles, check pin 12, 19 or 20 on U10 (which is the ADC0838 A/D converter), if you have less than 5V there then you have an obvious issue with the 5V logic supply. It could be the 5V reg, but more likely something is shorted (or very low impedance) on the 5V rail and pulling it down.

Make sure you are using an appropriate ground reference to make these measurements. The Tab on IC5 (the 5V Reg) is a good place to pick up a logic ground if you haven't got one already as are pins 4 & 9 on the D9 connector on the back panel.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of