When the power goes out the UPS SMT2200 doesn't supply power to the plugs in back. Not sure if it's a setting or something else. Any help would be greatly appreciated. Thank you!
Model=SMT2200
Serial No.=AS1415140057
Firmware=UPS 08.8
Batteries=100%
Load=18%
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:55 PM . Last Modified: 2024-03-19 03:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:55 PM . Last Modified: 2024-03-19 03:05 AM
Please let me know about this. I think you need to replace the batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:55 PM . Last Modified: 2024-03-19 03:05 AM
Hi,
If you remove the load, remove AC from the UPS, and check the output with a voltmeter, is the UPS providing AC? If so, have you replaced the batteries? Based on the serial number, the UPS is six years old. If the batteries have not been replaced, they may read 100 percent charge, but the voltage may drop rapidly once the load is applied and the load is powered off.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:55 PM . Last Modified: 2024-03-19 03:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:55 PM . Last Modified: 2024-03-19 03:05 AM
Please let me know about this. I think you need to replace the batteries.