APC Symmetra PX160 short-time load drop

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Symmetra PX160 short-time load drop
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:45 AM . Last Modified: ‎2024-02-14 06:05 AM

0 Likes
1
594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:45 AM . Last Modified: ‎2024-02-14 06:05 AM

APC Symmetra PX160 short-time load drop

 

Hi, All.

There is one small (up 70kW of IT Load) DC with two independent utility source followed by ATys m ATS and Symmetra PX160 UPS for protect critical load.  

Some weeks ago, all IT load was dropped by Symmetra for 5-10 seconds.
This incident coinced with some issues at 10kV side and loss of Source 1 (for 2-3 hrs).
Some anomalies also expirienced on Source 2 at the same time (input power troubles were recovered in CRACS control unit logs), but no longer than 20-30 second and therefore wasn't registered by DataCenter Expert monitoring system (poll period = 1 minutes).

All load (IT under UPS and CRACS without UPS) was on the Source 2 at the time of issues.

So, all critical load was unexpectedly dropped for short time period, but no alarm events there found at Symmetra's PX display as no events in event.txt file downloaded from NMC. Only usual NTP updates..

Symmetra MIM logs shows some alarm messages (quoted below)
Any idea or suggestions? Thanx
 0600D07F EXSG  D Operate Q003 ok                          YY/MM/DD 09:47:14 654
0900A05E IM    A IM oper. mode: Shift to ONLINE           YY/MM/DD 09:47:14 628
0100D13E IM    D TIM has SBS on                           YY/MM/DD 09:47:14 628
0100A12E IM    A TIM has Inverter on                      YY/MM/DD 09:47:14 628
0100D57E IM    D Inverter sync. error                     YY/MM/DD 09:47:12 672
0280D24E PM 08 D Output RMS voltage fail                  YY/MM/DD 09:47:11 984
0280D23E PM 08 D Inverter RMS voltage fail                YY/MM/DD 09:47:11 984
0270D24E PM 07 D Output RMS voltage fail                  YY/MM/DD 09:47:11 931
0270D23E PM 07 D Inverter RMS voltage fail                YY/MM/DD 09:47:11 931
0260D24E PM 06 D Output RMS voltage fail                  YY/MM/DD 09:47:11 877
0260D23E PM 06 D Inverter RMS voltage fail                YY/MM/DD 09:47:11 877
0250D24E PM 05 D Output RMS voltage fail                  YY/MM/DD 09:47:11 825
0250D23E PM 05 D Inverter RMS voltage fail                YY/MM/DD 09:47:11 825
0240D24E PM 04 D Output RMS voltage fail                  YY/MM/DD 09:47:11 772
0240D23E PM 04 D Inverter RMS voltage fail                YY/MM/DD 09:47:11 772
0500A32E SBS   A Backfeed Contactor closed                YY/MM/DD 09:47:11 704
02A0D24E PM 10 D Output RMS voltage fail                  YY/MM/DD 09:47:11 672
02A0D23E PM 10 D Inverter RMS voltage fail                YY/MM/DD 09:47:11 672
0100D04E IM    D Output voltage error                     YY/MM/DD 09:47:11 624
0290D24E PM 09 D Output RMS voltage fail                  YY/MM/DD 09:47:11 619
0290D23E PM 09 D Inverter RMS voltage fail                YY/MM/DD 09:47:11 619
0100D02E IM    D Bypass voltage error                     YY/MM/DD 09:47:09 668
0240A24E PM 04 A Output RMS voltage fail                  YY/MM/DD 09:47:09 420
0240A23E PM 04 A Inverter RMS voltage fail                YY/MM/DD 09:47:09 420
0500D32E SBS   D Backfeed Contactor closed                YY/MM/DD 09:47:09 352
02A0A24E PM 10 A Output RMS voltage fail                  YY/MM/DD 09:47:09 315
02A0A23E PM 10 A Inverter RMS voltage fail                YY/MM/DD 09:47:09 315
0290A24E PM 09 A Output RMS voltage fail                  YY/MM/DD 09:47:09 263
0290A23E PM 09 A Inverter RMS voltage fail                YY/MM/DD 09:47:09 263
0280A24E PM 08 A Output RMS voltage fail                  YY/MM/DD 09:47:09 210
0280A23E PM 08 A Inverter RMS voltage fail                YY/MM/DD 09:47:09 210
0270A24E PM 07 A Output RMS voltage fail                  YY/MM/DD 09:47:09 158
0270A23E PM 07 A Inverter RMS voltage fail                YY/MM/DD 09:47:09 158
0260A24E PM 06 A Output RMS voltage fail                  YY/MM/DD 09:47:09 105
0260A23E PM 06 A Inverter RMS voltage fail                YY/MM/DD 09:47:09 105
0250A24E PM 05 A Output RMS voltage fail                  YY/MM/DD 09:47:09 053
0250A23E PM 05 A Inverter RMS voltage fail                YY/MM/DD 09:47:09 053
0600A07F EXSG  A Operate Q003 ok                          YY/MM/DD 09:47:08 966
0900A07E IM    A IM oper. mode: Shift to TEMP BYPASS      YY/MM/DD 09:47:08 924
0100A13E IM    A TIM has SBS on                           YY/MM/DD 09:47:08 924
0100D12E IM    D TIM has Inverter off                     YY/MM/DD 09:47:08 924
0100A57E IM    A Inverter sync. error                     YY/MM/DD 09:47:08 510



Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:45 AM . Last Modified: ‎2024-01-31 03:00 AM

0 Likes
0
594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:45 AM . Last Modified: ‎2024-01-31 03:00 AM

Hi,

Sorry for the inconvenience. I have asked that someone from regional 3 phase support team contact you concerning this matter.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:45 AM . Last Modified: ‎2024-01-31 03:00 AM

0 Likes
0
595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:45 AM . Last Modified: ‎2024-01-31 03:00 AM

Hi,

Sorry for the inconvenience. I have asked that someone from regional 3 phase support team contact you concerning this matter.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now