APC Symmetra LX Both Battery Modules Bad?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Symmetra LX Both Battery Modules Bad?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:56 AM . Last Modified: ‎2024-03-12 01:31 AM

0 Likes
2
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:56 AM . Last Modified: ‎2024-03-12 01:31 AM

APC Symmetra LX Both Battery Modules Bad?

My weekend was single-handedly ruined by my Symmetra unit sending out SNMP alerts that the battery was discharging even though the power was on.  From the logs it looked like the unit was in a self-test loop.  Every minute or so it would self test over and over again until the battery charge was at zero.  I called support this morning and the tech led me through diagnostics and came to the conclusion that both battery modules were bad and needed to be replaced.  The management console listed both batteries as good and the unit is less than 3 years old.  The tech said that diagnostics showed the batteries were over 50 degrees-C and that may have led to the failure.  That's odd because the ambient temp of the room is about 23 C and the internal temp of the APC is reporting 39 C.

Now I'm in the uncomfortable position of running my environment in bypass until the replacement batteries are overnighted.  The reason I purchased this unit is because of the redundancy aspect.  Redundancy does no one any good when both parts die at the same time.  This seems VERY odd to me.  Is this normal for both battery modules to go bad at the same time?

With the unit in bypass, the battery is recharging from 0% and 2 hours later it's at 30%.  Do I really need new batteries?  What exactly happened here?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:56 AM . Last Modified: ‎2024-03-12 01:30 AM

0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:56 AM . Last Modified: ‎2024-03-12 01:30 AM

I know this may not be much consolation, but I had a similar experience, except I had FOUR sybt5's in the UPS frame flagged as bad simultaneously. All had to get replaced. A couple of  weekends back I had one battery out of two in an adjacent LX melt down (thermal runaway) quite badly and the UPS'  intelligence modules put the UPS into bypass automatically to shut down the charging. I swapped out that battery , UPS came back online and am rebuilding the other one so back in business.... except for the fact that the Battery bus voltage is falsely being reported as 146.4 V DC on the Powerview when it actually measures 136 or so (which is normal)... not sure what's up with that !  Unfortunately short of doing a MIM log dump there is no way of getting battery temperature information out of the LX other than to physically put your hands on the modules ! Best of luck,

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:56 AM . Last Modified: ‎2024-03-12 01:30 AM

0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:56 AM . Last Modified: ‎2024-03-12 01:30 AM

The problem ended up being the L2 power module.  I was wondering why he was so apologetic on the phone.  I had no idea the APC reps actively monitor this forum.  Good job guys.  My frustration wasn't aimed at the tech, I just wanted to know from the community if it was common for both batteries to die at the same time.  That was very odd.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:56 AM . Last Modified: ‎2024-03-12 01:30 AM

0 Likes
0
823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:56 AM . Last Modified: ‎2024-03-12 01:30 AM

I know this may not be much consolation, but I had a similar experience, except I had FOUR sybt5's in the UPS frame flagged as bad simultaneously. All had to get replaced. A couple of  weekends back I had one battery out of two in an adjacent LX melt down (thermal runaway) quite badly and the UPS'  intelligence modules put the UPS into bypass automatically to shut down the charging. I swapped out that battery , UPS came back online and am rebuilding the other one so back in business.... except for the fact that the Battery bus voltage is falsely being reported as 146.4 V DC on the Powerview when it actually measures 136 or so (which is normal)... not sure what's up with that !  Unfortunately short of doing a MIM log dump there is no way of getting battery temperature information out of the LX other than to physically put your hands on the modules ! Best of luck,

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of