APC Smart-UPS X 3000VA

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS X 3000VA
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

0 Likes
7
1204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

APC Smart-UPS X 3000VA

I have a one APC Smart-UPS X 3000VA (part # SMX3000RMLV2U) I tested at my main office and it powered up and worked fine. I powered it down and took it to a remote office, installed and powered it back up. When I powered up I got a soft start fault error. Since this location is an hour away I plugged a usb cable into it and one of the local servers in hopes of getting some diagnostics off of it later. What's wrong with this unit? How can I get diagnostic information off of it without a network management card?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • smart_ups_x_3000
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 01:38 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 01:38 AM

Looks like your UPS already has the latest firmware version frown - UPS 7.4 for ID1003 is indeed the latest already. I would say since you are at the latest and there was no change after you did the braindead reset, then the entire UPS should be replaced under warranty.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

You'll want to grab PowerChute Business Edition which supports the USB connection for this UPS type. That is available here @ http://www.apc.com/tools/download/index.cfm

Let's get PowerChute Business Edition Agent installed which you can access hopefully through that remote server since it is locally attached to the UPS via USB. Let's check the status/event log of the UPS through there and I think this could be related to when you moved it. It was suggested to me, assuming the UPS is on, to run a UPS self test diagnostic and see if it clears.

The next step if that does not do anything would be to braindead the UPS which requires local access to the unit and will reset it.

Keep in mind too depending on the UPS status and issue, if the server is plugged into the UPS for power and the UPS turns off, then that may not work out well laughing

Let me know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

Event log has 3 entries, 1) monitoring started 2) communication established 3) TurnOff delay was adjusted. Self-test status and last runtime calibration status show Refused.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

Hmm OK. Next step would be to "braindead" it which will require you to go over to it, turn off and remove any load. Then, turn the UPS off, disconnect the USB cable, unplug it from the wall, and remove the battery for several seconds while holding the power button down after the battery is removed. This will discharge all capacitors and reset the UPS intelligence and clear out any issues that may cause this. If it still does not work, then it may need to be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 02:41 AM

I ran through all of your steps, when I turn it back on I'm still getting refused for both my self-test status and runtime calibration. If something needs to be replaced would it be the battery or the entire unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 01:38 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 01:38 AM

We'd recommend the entire unit but I just learned this could be due to older firmware. Can you find the UPS firmware version from PowerChute and let me know what it is? It should say something like UPS 09.1 or something and possibly have an ID listed like ID19.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 01:38 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 01:38 AM

 

UPS 07.4 / MCU 07.4 (1003 - 😎
Product Version

  9.1.1.604

I'll check and try to apply the latest firmware if you think that will help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 01:38 AM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:52 AM . Last Modified: ‎2024-03-12 01:38 AM

Looks like your UPS already has the latest firmware version frown - UPS 7.4 for ID1003 is indeed the latest already. I would say since you are at the latest and there was no change after you did the braindead reset, then the entire UPS should be replaced under warranty.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of