APC Smart-UPS VT alarms

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS VT alarms
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:40 AM

0 Likes
4
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:40 AM

APC Smart-UPS VT alarms

Lately I'm getting the following alerts:

Environment: A fault no longer exists for integrated Environmental Monitor Output Relay (Int Relay at Int Relay Location).
UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
Environment: A fault exists for integrated Environmental Monitor Output Relay (Int Relay at Int Relay Location).
UPS: An input voltage or frequency problem prevents switching to bypass mode.

Getting them every few minutes. Attached a log so you can see. Anybody know why this is happening?

Message was edited by: ricardo.pereira77

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:39 AM

0 Likes
0
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:39 AM

you'll need to look and see if the input voltage is fluctuating. what it is saying is the input voltage from your mains supply is going in an out of the bypass transfer range so depending on other settings, if the voltage is out of range and the UPS has to go to bypass, it won't be able to.

this can be reviewed with the data log on the network management card as well.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:40 AM

0 Likes
0
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:40 AM

Tried to attach the log but was unable. Here is the log https://www.dropbox.com/s/4xptts0etm8mpa2/Log_UPS-BMF.xlsx

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:39 AM

0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:39 AM

hello,

what this is telling me is that the Output Relay on your AP9619 (most likely what you have) must be mapped to activate when you have a fault or something like that.

log in via the web UI and go to the Environment Tab->Output Relay and see what you have selected under Mapping and adjust it accordingly. If you don't use the output relay, you can just uncheck all of the events for mapping.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:39 AM

0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:39 AM

What about the other alert that keeps popping up?

UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
UPS: An input voltage or frequency problem prevents switching to bypass mode.

Message was edited by: ricardo.pereira77

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:39 AM

0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:40 AM . Last Modified: ‎2024-03-19 12:39 AM

you'll need to look and see if the input voltage is fluctuating. what it is saying is the input voltage from your mains supply is going in an out of the bypass transfer range so depending on other settings, if the voltage is out of range and the UPS has to go to bypass, it won't be able to.

this can be reviewed with the data log on the network management card as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login