APC Smart-UPS RT 2000VA RM 230V - Will Not Power Up

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS RT 2000VA RM 230V - Will Not Power Up
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:15 AM . Last Modified: ‎2024-03-18 03:40 AM

0 Likes
2
1979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:15 AM . Last Modified: ‎2024-03-18 03:40 AM

APC Smart-UPS RT 2000VA RM 230V - Will Not Power Up

We have an APC Smart-UPS RT 2000VA RM 230V.

Following a number of short mains disturbances at the weekend, the UPS will now not power up.

This is what I have tried so far;

  • Checked all connections are secure
  • Ensured the breaker on the rear panel had not tripped
  • Changed the fuse in the mains cable
  • Changed the mains cable
  • Put a meter across the battery plug (the reading was a steady 110v)
  • Left it plugged into the mains for two days

I also put a meter across two capacitors in the power supply, which also gave a reading of 110v. This may or may not be a fault, but when the battery, mains or both are disconnected, the capacitors discharge very quickly and sit at around 30v.

Occasionally, pressing the on / test button makes the fans start up and there is a brief beep for about a second...before the UPS is dead again. This happens on mains with the battery connected, on mains with the battery disconnected, and when the UPS has no mains connected (just the battery).

It seems to me like there may be a power supply fault with the UPS itself. If left on mains for a minute or two, the fans try to spin but are unable to - it is as if they are not getting enough power and make a ticking noise, but do not actually manage to spin. During the brief burst of power sometimes (as mentioned above), both fans spin up - which confirms they do work.

The batteries are good, although they may be low on charge due to the mains problems over the weekend.

Can anyone assist with any further suggestions?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2000va
  • 230v
  • apc
  • dead
  • rm
  • rt
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:15 AM . Last Modified: ‎2024-03-18 03:40 AM

0 Likes
0
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:15 AM . Last Modified: ‎2024-03-18 03:40 AM

Hello Shannon

Thanks for your reply.

I will get the model and serial numbers as soon as I have access to the UPS again. Over the weekend, I may try slowly charging the batteries and seeing if that works.

The batteries were only replaced a year ago using a genuine APC pack.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:15 AM . Last Modified: ‎2024-03-18 03:40 AM

0 Likes
0
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:15 AM . Last Modified: ‎2024-03-18 03:40 AM

Hello Damien,

I am sorry that you are having issues with your UPS. 

So that I can give you the best support, I need to get more information: What is the model and serial number of you UPS?

At this point, from what you are describing, you probably have bad battery in the UPS. You probably have an older smart ups that will not turn on without good batteries. 

Thanks,
Shanon

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:15 AM . Last Modified: ‎2024-03-18 03:40 AM

0 Likes
0
1979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:15 AM . Last Modified: ‎2024-03-18 03:40 AM

Hello Shannon

Thanks for your reply.

I will get the model and serial numbers as soon as I have access to the UPS again. Over the weekend, I may try slowly charging the batteries and seeing if that works.

The batteries were only replaced a year ago using a genuine APC pack.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore