Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

APC ShareUPS - Smart Cables

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC ShareUPS - Smart Cables
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

0 Likes
3
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

APC ShareUPS - Smart Cables

Hey all,

I have a SmartUPS 1400 that is connected to the 8 port Share Ups. My cable from the Smart Ups is a Smart Cable 940-0024. I also have 5 other of the 940-0024 Smart Cables. We recently moved and my other servers that are connected through ports 2-6 on the Share Ups report faults when using the Smart Cable.

I was pretty certain I used all Smart Cables for all servers before the move as I could not find any basic cables packed away anywhere.

I was on the phone with Tech Support for awhile and they thought that I could use either a Smart or Basic cable but were not able to resolve my issue.

My configuration is all Windows 2003 Server and 1 Windows 2000 Server. I am using the PowerChute Business Edition Version 7, the server/agent/console on my Server that is on port 1. The rest of them just have the PowerChute Business Edition version 7 Agent on them and they are set for "ShareUps" I tried switching them between "Smart and Basic" as well.

They all report running on battery and threshold time on battery exceeded.

Any ideas, do I in fact need to get 5 of the 940-0020 Basic cables? They are pretty expensive so I don't want to buy them if I don't need them.

Thanks in advance.

Bryan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

0 Likes
0
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

Hey all,

I have a SmartUPS 1400 that is connected to the 8 port Share Ups. My cable from the Smart Ups is a Smart Cable 940-0024. I also have 5 other of the 940-0024 Smart Cables. We recently moved and my other servers that are connected through ports 2-6 on the Share Ups report faults when using the Smart Cable.

I was pretty certain I used all Smart Cables for all servers before the move as I could not find any basic cables packed away anywhere.

I was on the phone with Tech Support for awhile and they thought that I could use either a Smart or Basic cable but were not able to resolve my issue.

My configuration is all Windows 2003 Server and 1 Windows 2000 Server. I am using the PowerChute Business Edition Version 7, the server/agent/console on my Server that is on port 1. The rest of them just have the PowerChute Business Edition version 7 Agent on them and they are set for "ShareUps" I tried switching them between "Smart and Basic" as well.

They all report running on battery and threshold time on battery exceeded.

Any ideas, do I in fact need to get 5 of the 940-0020 Basic cables? They are pretty expensive so I don't want to buy them if I don't need them.

Thanks in advance.

Bryan

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

0 Likes
0
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

Ok Thanks! I didn't know about these network cards, do they do the same thing basically as the Share Ups?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

0 Likes
0
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

With a network card in the UPS, you can install PowerChute Network Shutdown (for free) on each server and have them all shutdown gracefully when you want them to (for a number of different scenarios). The network cards have a lot more functionality than PCBE does, especially since most of your connections on the Share-UPS are simple signaling - you can have a look at the interfaces of the different cards and see the features for yourself here (check out the top 2): http://testdrive.apc.com/card.htm

And you don't need to worry about a bunch of serial cables all over the place!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:41 PM . Last Modified: ‎2024-03-14 01:23 AM

Hey all,

I have a SmartUPS 1400 that is connected to the 8 port Share Ups. My cable from the Smart Ups is a Smart Cable 940-0024. I also have 5 other of the 940-0024 Smart Cables. We recently moved and my other servers that are connected through ports 2-6 on the Share Ups report faults when using the Smart Cable.

I was pretty certain I used all Smart Cables for all servers before the move as I could not find any basic cables packed away anywhere.

I was on the phone with Tech Support for awhile and they thought that I could use either a Smart or Basic cable but were not able to resolve my issue.

My configuration is all Windows 2003 Server and 1 Windows 2000 Server. I am using the PowerChute Business Edition Version 7, the server/agent/console on my Server that is on port 1. The rest of them just have the PowerChute Business Edition version 7 Agent on them and they are set for "ShareUps" I tried switching them between "Smart and Basic" as well.

They all report running on battery and threshold time on battery exceeded.

Any ideas, do I in fact need to get 5 of the 940-0020 Basic cables? They are pretty expensive so I don't want to buy them if I don't need them.

Thanks in advance.

Bryan

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore