APC SURTD5000XLI battery led blinking green

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SURTD5000XLI battery led blinking green
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

0 Likes
1
5128
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

APC SURTD5000XLI battery led blinking green

Hi All,

I have a APC SURTD5000XLI UPS with the battery led blinking green and web status showing critical alarm battery discharged.

After replacing the batteries, the fault is still the same. We performed self-test, test passed. However, the run time is approximately 2 minutes.

The status shows batteries are charging and run time is very little.  We have an extra battery pack connected and the load is about 41%.


Please advise the next course of action. This UPS is critical to operations and cannot afford to be down.

The serial number is NS0807029920.


Please advise on the procedures to perform manual battery calibration or remedy action.


Many thanks in advance.


Cheers


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

0 Likes
0
5125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

I assume by battery LED, you mean the battery bar graph is flashing. This means your runtime is within two minutes of low battery signaling time which makes sense since you're runtime is two minutes and the low battery time is by default two minutes as well. So basically, you probably do need to do a calibration to update the runtime with the new batteries.

You can do this within the network management card but I am not sure what the result would be since runtime reported is so low - it might not even try.

Here is how to do a manual calibration:

A manual runtime calibration is the process of completely discharging a battery by simulating a power outage (pulling the plug of the UPS from the AC power circuit or tripping upstream breaker). This process is sometimes necessary in order to reset the estimated runtime calculation if it does not appear to be correct. In order for the calibration to work properly, and for the runtime to be estimated correctly, there are four conditions which must be met when initiating and running the calibration. They are as follows:


1. Battery must be at 100% capacity when the Runtime Calibration is initiated/started.

2. The UPS must have at least a 30% load on it during the calibration.

3. The load cannot fluctuate more than +/- 5% during the calibration.

4. The battery must be discharged to at least 25% capacity (it is best to allow the UPS to shut off due to a discharged battery).


In addition to the above conditions, any UPS monitoring/shutdown software should be stopped from running in the background, management card uninstalled, and the serial cable should be detached from the UPS. This is necessary in order to prevent the software from shutting down the server/UPS due to an on-battery or low-battery condition.


So, you may need to do this during some downtime..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

0 Likes
0
5126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

I assume by battery LED, you mean the battery bar graph is flashing. This means your runtime is within two minutes of low battery signaling time which makes sense since you're runtime is two minutes and the low battery time is by default two minutes as well. So basically, you probably do need to do a calibration to update the runtime with the new batteries.

You can do this within the network management card but I am not sure what the result would be since runtime reported is so low - it might not even try.

Here is how to do a manual calibration:

A manual runtime calibration is the process of completely discharging a battery by simulating a power outage (pulling the plug of the UPS from the AC power circuit or tripping upstream breaker). This process is sometimes necessary in order to reset the estimated runtime calculation if it does not appear to be correct. In order for the calibration to work properly, and for the runtime to be estimated correctly, there are four conditions which must be met when initiating and running the calibration. They are as follows:


1. Battery must be at 100% capacity when the Runtime Calibration is initiated/started.

2. The UPS must have at least a 30% load on it during the calibration.

3. The load cannot fluctuate more than +/- 5% during the calibration.

4. The battery must be discharged to at least 25% capacity (it is best to allow the UPS to shut off due to a discharged battery).


In addition to the above conditions, any UPS monitoring/shutdown software should be stopped from running in the background, management card uninstalled, and the serial cable should be detached from the UPS. This is necessary in order to prevent the software from shutting down the server/UPS due to an on-battery or low-battery condition.


So, you may need to do this during some downtime..

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of