APC SUA1500i with AP9619 output connectors always powered

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SUA1500i with AP9619 output connectors always powered
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:10 AM

0 Likes
8
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:10 AM

APC SUA1500i with AP9619 output connectors always powered

Hello.

I have a SUA1500i with AP9619 management card, works like a charm but there is one thing:

When switching off the ups everything seems to work just fine, all lights in the front panel are switched off, some clicking noises as it but: The output connectors are still powered and there is still the light on the ethernet port of the AP9619 until the mains are disconnected. As far as I remember that is not the way it used to be or should be?

Is it possible that this behaviour has something to do with the AP 9619 card? Is this by design and I just did not recognize it earlier?

Any help is appreciated- thanks in advance!

Lutz

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • network-management-card
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

Hi Angela,

thanks for your answer. I'm pretty sure that this unit did work like it's supposed to be a while ago. But I figured there might a little chance that this might have been kind of a "special mode" that was possibly associated with adding the nmc.

Actually I think it might be a welded relay, will things get checked!

Thanks a lot! Best regards

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:10 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:10 AM

Anything in the UPS SmartSlot, like the AP9619, will remain energized until the UPS completely de-energizes which happens about 8-10 minutes after AC power is missing. Or, you can manually do this process, which we usually refer to as braindeading, by holding the off button down on the front panel for a few seconds, assuming AC power is not present at the time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

Thanks for your answer.

The management card isn't the thing I'm worried about too much. But is it normal that as soon as I connect the (switched off) ups to a power chord all power connectors have power with the ups still being switched off?

Best regards

Lutz

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

Hi Lutz,

Yes it is, as soon as the UPS is connected to power, it is now energized, so the SmartSlot device is, though you have to command the output of the UPS (AKA the outlets) on. This is just the reverse of what I explained and is all as it should be. 

Let me know if I can clarify further.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

Hi Angela,

I'm sorry, but yes, it would be nice if you could clarify. You wrote

".... though you have to command the output of the UPS (AKA the outlets) on. ....."

My question is:

My UPS switched off, power cable disconnected

Putting in mains power cable

UPS still switched off, no lights on the front, no button pressed BUT

ALL OUTLETS are ON

I think you meant with "have to command the output on" pushing the "ON" button? I don't have to, my outlets are on as soon as the mains cable is connected to the UPS- no matter in which condition the UPS is.

Thanks in advance, best regards

Lutz

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

Hi Lutz,

This may be a concern on the UPS side versus the AP9619 then. But, are you simulating a power outage? How is the UPS being turned off - manually, or due to a low battery condition? If it is a low battery condition, then the UPS design is to turn on as soon as AC power is restored to provide power ASAP to your equipment/outlets without you having to be there to turn it on.

If you're turning it off manually or by some other means, depending on how, it may turn off and stay off until you turn it back on.

So, can you clarify in the above scenario(s), how is the UPS turning being turned off when you say "My UPS Switched off, power cable disconnected." If it is because you unplugged the UPS to test it and let it run until it turned off, that would be due to "low battery" and connecting the power cable again would restore AC power and turn the outlets on as you did not manually turn the UPS off in that scenario (using a software command or power button).

Hope that helps and makes sense embarassed

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

Hi Angela,

thanks a lot for your answer!

To clarify:

I can switch off the UPS via button or via network-management-card (battery full, no power fail, mains cable plugged in), all lights go off, nmc reports "UPS: The output power is turned off." but the outlets are still ON. First disconnecting the mains cable "switches" the outlets off.

And putting the mains cable into the fully charged, beforehand manually (by pressing the off- button) switched off UPS "switches" the outlets ON at once without having to push the power button.

Hope it makes sense now

Thanks in advance, best regards smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:23 PM . Last Modified: ‎2024-03-19 12:09 AM

If the UPS reports that "the UPS output power is turned off" and then the outlets are still on, then it sounds like there is a problem with the UPS (maybe the output relay?). You should be able to have the output turned off but the unit still plugged in frown 

Did this ever work properly or you're not sure?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

0 Likes
0
1233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:24 PM . Last Modified: ‎2024-03-19 12:09 AM

Hi Angela,

thanks for your answer. I'm pretty sure that this unit did work like it's supposed to be a while ago. But I figured there might a little chance that this might have been kind of a "special mode" that was possibly associated with adding the nmc.

Actually I think it might be a welded relay, will things get checked!

Thanks a lot! Best regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore