Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

APC SUA1500i: output connectors loose/moving slightly

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SUA1500i: output connectors loose/moving slightly
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
davidoffc_apc
Ensign davidoffc_apc
Ensign

Posted: ‎2021-06-29 07:50 AM

0 Likes
4
841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 07:50 AM

APC SUA1500i: output connectors loose/moving slightly

This was originally posted on APC forums on 3/14/2014


Hi there,


I have an APC UPS SUA1500i, bought it approximately three years ago.


At the very beginning when I started connecting the cables to connect all the equipment I noticed that the rear output connectors/receptacles(?) -- there are 8 of them -- are slightly moving. Tried using the cables supplied with the UPS and also bought some more, and noticed that at the slightest pull or touch they just simply move, causing electricity fall-outs, and could even fall out. And sometimes, when vacuum-cleaning around the UPS and its cables, should I touch any of the output cables, electricity to device(s) falls-out, sometimes there’s even that electrical ‘buzzing’ sound.


What use is the UPS when it has electricity but the output cables are moving and do not provide proper electrical supply? Three SATA disks were destroyed in the recent power fall-out.


Also, what is the meaning of all the LED lights on the right blinking very fast? If I work with the laptop, they aren't lit, but if I turn on the desktop computer, they start blinking.


Anyone else had this issue? Help me, please.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • blinking
  • connectors
  • fall-out
  • leds
  • rear
  • receptacles
  • sua1500i
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
davidoffc_apc
Ensign davidoffc_apc
Ensign

Posted: ‎2021-06-29 07:50 AM

0 Likes
1
841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 07:50 AM

This was originally posted on APC forums on 3/24/2014


An update to my issue with loose cables...

What I did to fix this is with plastic furniture levelers. Strange, but it works! Cables don't move any longer.

See Answer In Context

Reply
Share
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:50 AM

0 Likes
0
841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 07:50 AM

This reply was originally posted by Angela on APC forums on 3/17/2014


I can tell you about the flashing battery bar graph here...

Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric ITB

Usually this means that there is a setting/configuration issue or that the runtime is low if you haven't changed any settings recently.

Reply
Share
davidoffc_apc
Ensign davidoffc_apc
Ensign

Posted: ‎2021-06-29 07:50 AM

0 Likes
0
841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 07:50 AM

This was originally posted on APC forums on 3/24/2014


Thank you for your answer, Angela. Have to read the document and try what can be done.

Reply
Share
davidoffc_apc
Ensign davidoffc_apc
Ensign

Posted: ‎2021-06-29 07:50 AM

0 Likes
1
842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 07:50 AM

This was originally posted on APC forums on 3/24/2014


An update to my issue with loose cables...

What I did to fix this is with plastic furniture levelers. Strange, but it works! Cables don't move any longer.

Reply
Share
kiwi4000
kiwi4000
Cadet

Posted: ‎2022-04-07 12:15 AM

In response to davidoffc_apc
0 Likes
0
648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2022-04-07 12:15 AM

Hi Could you please post a link to the plastic furniture levelers?

  • Tags:
  • english
Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc