when i slowly cut off the main power from my apc 1500 ups its all 6 light on, beep and go to zero battery show. The batteries are ok when i turned off the ups and on again its shows the correct battery status.
If the main power suddenly cut off then its working normally but when i slowly cut off the power then it show the problem... please help!!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:40 PM . Last Modified: 2024-03-06 11:52 PM
The AVR relay is faulty (usually welded). The unit will need to be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:40 PM . Last Modified: 2024-03-06 11:52 PM
Hello Moshin,
What do you mean by "slowly cut off the power"?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:40 PM . Last Modified: 2024-03-06 11:52 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:40 PM . Last Modified: 2024-03-06 11:52 PM
means I can cutoff the power through switch for checking. so when i smoothly shutoff the switch then the problem occurred and when I suddenly or quickly shutoff the switch its working normally.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:40 PM . Last Modified: 2024-03-06 11:52 PM
The AVR relay is faulty (usually welded). The unit will need to be replaced.