APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-07-07 10:50 PM . Last Modified: 2024-03-01 12:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:50 PM . Last Modified: 2024-03-01 12:22 AM
The problem I am having is when I turn the unit off there is still power going to the plugins. I can pull the unit's cord from the wall power (commercial) and it supplies power to the two computers just fine. I can not figure out why all of sudden the plugins are staying on when I turn the power off with the switch. This is definitely an older unit. Probably about 12 years old but if it still works I can not see replacing it. Fortunately it is still relialble if there is a power outage.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:50 PM . Last Modified: 2024-03-01 12:22 AM
When you hit the button the main board triggers the relay that actually switches on/off. Your issue could be cause by the relay. The UPS Should be safe to continue using. To turn the UPS off you could plug the UPS into a power strip. (I know we do not normally recommend using a power strip with a UPS but in this case it is a good solution.) To power down hit the power off button on the UPS and then kill AC to the UPS via the strip.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:50 PM . Last Modified: 2024-03-01 12:22 AM
When you press the power off button does the unit continue to run on AC or does it switch to battery output? Do any of the LEDs on the front panel change?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:50 PM . Last Modified: 2024-03-01 12:22 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:50 PM . Last Modified: 2024-03-01 12:22 AM
When powered down all the leds turn off. It is running off of AC when turned off. If I turn the unit off and then pull the ups power plug from the commercial outlet everything powers down. The last time I turned it off it worked properly and all power including AC was cut off. For some reason it does work correctly once and a while. Is there something that could be plugged in that prevents the ups from powering down? I have tried unplugging everything and it does not seem to make any difference. Fortunately in about 1 hour I am leaving on a 10 day sea kayaking trip in Prince William Sound so I can put this on the back burner a while.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:50 PM . Last Modified: 2024-03-01 12:22 AM
When you hit the button the main board triggers the relay that actually switches on/off. Your issue could be cause by the relay. The UPS Should be safe to continue using. To turn the UPS off you could plug the UPS into a power strip. (I know we do not normally recommend using a power strip with a UPS but in this case it is a good solution.) To power down hit the power off button on the UPS and then kill AC to the UPS via the strip.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.