Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
APC SRT10RMKXLI Error P.15
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. Apologies for the late revert. Upon checking, Error P.15 has something to do with the Bypass Power Factor Correction (PFC) Relay. The Battery PFC Relay was welded.
To recover from the fault, you can clear the alarm and turn the UPS/output ON via the display. If the alarm cannot be cleared, you can do a brain dead on the UPS. If it cannot be cleared, the UPS would need to be replaced.
For SMC, SMT, SMX, and SRT Units: 1) Turn off and unplug UPS from the wall 2) Disconnect Battery 3) You may hear an audible "click" from the UPS. 4) Reconnect battery, plug unit back in the wall, and turn UPS back on.