APC SMX750NMC UPS - Hot Swap Batteries - Equal to a Manual Bypass Switch ?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
No. When a UPS is placed in bypass, the UPS bypasses all charging and conditioning. When a battery is hot-swapped, the UPS is still conditioning the output.
In either case if AC is lost while the battery is disconnected or while in bypass the load will drop.