APC Rack 1000V Smart-UPS won't turn on
I just got a new SUA1000RM2U Smart-UPS from a guy on CL and the item was never used NIB. Now, I brought it home and plugged it in but it did not turn on. I let it charge for about an hour, still did not turn on. I let it charge overnight (~13 hours later) and it still did not turn on this morning. Here's what I tried:
Unplugged it and tried to turn it on: Didn't work
Plugged it in, disconnected batteries and tried to turn it on: Didn't work
Held power off button after unplugging: Didn't work, no notifications or beeps
Held power on button for 30 seconds (plugged in and not plugged in): Nothing happened
I've owned and worked with UPSs in the past so this isn't foreign territory but I know its not supposed to be this difficult to turn on. I've also measured the voltage across the battery and it reads ~2.7v. I also measured the voltage across the charging points (battery connector's mate) when the unit was plugged in and it read 0.2v which doesn't seem right at all. I was wondering what else I could do or if there was something I'm missing. Thank you!
- Labels:
-
Smart-UPS & Symmetra LX | RM
- Tags:
- smart-ups
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:52 AM . Last Modified: 2024-03-18 03:04 AM
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:52 AM . Last Modified: 2024-03-18 03:04 AM
You need a new battery. Those units need to see a reasonable battery voltage to start the electronics. Once it is started it fires up the inverter and you get power from the mains, but it needs a battery to get it going. The battery in your unit is toast based on a 2.7V reading across the pack. Even if you could get it to start, the battery will be damaged beyond salvation.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:52 AM . Last Modified: 2024-03-18 03:04 AM
Brad,
Thank you for your response. I'll look into getting a replacement.