Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
APC PowerChute and SmartUPS over LAN
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0104:14 AM. Last Modified: 2024-03-0502:26 AM
It is not good practice to do this because the actual servers with PowerChute should be physically connected to the UPS with the management card you want to associate them with.
For instance, if Room 2's power goes out and a server connected in Room 1 is connected to the AP9630 in Room 2, it'd be commanded to turn off even though the UPS it is plugged into still has power.
It is recommended that either the servers be directly plugged in for power to the UPSs they are attached to or obtain an AP9630 for Room 1 or just leave it as is.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0104:14 AM. Last Modified: 2024-03-0502:26 AM
It is not good practice to do this because the actual servers with PowerChute should be physically connected to the UPS with the management card you want to associate them with.
For instance, if Room 2's power goes out and a server connected in Room 1 is connected to the AP9630 in Room 2, it'd be commanded to turn off even though the UPS it is plugged into still has power.
It is recommended that either the servers be directly plugged in for power to the UPSs they are attached to or obtain an AP9630 for Room 1 or just leave it as is.