Hi guys,
My APC: APC Smart-UPS 2200VA USB & Serial 230V
When i install APC PowerChute Business Edition Software on my server ( Window server 2008, 64bit) with Hyper-V installed, I get a error " THIS VERSION IS NOT SUPPORT HYPER-V" ?
have another Version support Hyper-V ?
OR IF i buy a UPS Network Management Card, can i resolve problem above ? i can install APC PowerChute Business Edition Software which not error " THIS VERSION IS NOT SUPPORT HYPER-V" ?
Please give me some information to resolve this error...
Thanks & best regards
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:00 PM . Last Modified: 2024-03-07 01:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:00 PM . Last Modified: 2024-03-07 01:39 AM
Thank for your reply, i picKed a winna
but i have a question about network management card...
IF i buy a network management card.
Must i buy a PowerChute Network Shutdown for Hyper-V - Single Physical Server License ?
Or use accompanying software of network management card, have it support Hyper-V ?
And shutdow process of window server have guest os on Hyper-V ?
Thanks & Best regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:00 PM . Last Modified: 2024-03-07 01:39 AM
yes, you must buy the PCNS for Hyper-V single server license. the free PCNS will not install on the system running Hyper-V.
also, to shutdown the guest OS, please see[this APC Knowledgebase|http://nam-en.apc.com/app/answers/detail/a_id/10381/].
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:00 PM . Last Modified: 2024-03-07 01:39 AM
yes, powerchute network shutdown is what you need for Hyper-V. you must use a network management card in conjunction with the specific powerchute network shutdown for hyper-v.
here is some helpful info on that -> http://www.apc.com/products/family/index.cfm?id=127
install documents -> http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SSPCNSHV&tab=documentation
also some knowledgebases:
http://nam-en.apc.com/app/answers/detail/a_id/10381/
http://nam-en.apc.com/app/answers/detail/a_id/10679/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:00 PM . Last Modified: 2024-03-07 01:39 AM
yes, powerchute network shutdown is what you need for Hyper-V. you must use a network management card in conjunction with the specific powerchute network shutdown for hyper-v.
here is some helpful info on that -> http://www.apc.com/products/family/index.cfm?id=127
install documents -> http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SSPCNSHV&tab=documentation
also some knowledgebases:
http://nam-en.apc.com/app/answers/detail/a_id/10381/
http://nam-en.apc.com/app/answers/detail/a_id/10679/
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:00 PM . Last Modified: 2024-03-07 01:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:00 PM . Last Modified: 2024-03-07 01:39 AM
Thank for your reply, i picKed a winna
but i have a question about network management card...
IF i buy a network management card.
Must i buy a PowerChute Network Shutdown for Hyper-V - Single Physical Server License ?
Or use accompanying software of network management card, have it support Hyper-V ?
And shutdow process of window server have guest os on Hyper-V ?
Thanks & Best regards