APC 7752 under frequency violation

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 7752 under frequency violation
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 07:10 AM . Last Modified: ‎2024-03-04 10:59 PM

0 Likes
4
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:10 AM . Last Modified: ‎2024-03-04 10:59 PM

APC 7752 under frequency violation

Hello, today I had a problem with the ATS AP7752 

Source A is connected to  UPS 1 

Source B is connected to  UPS 2 

frequency deviation is set at 2 Hz 

Preferred source is set to none

voltage transfer range is set to medium

The two UPS are connected to the commercial AC and they switch to a generator if a power outage occurs, the problem happen when the UPS switch to commercial AC again after the power outage, the ATS drops the load and show 0 A in the display, to solve this I had to press the front panel button to switch the preferred source as you can see in the last picture.

Any idea what could be the problem?

2ymptPvuxsQWPgWelyxfug%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png2ymptPvuxsQWPgWelyxfug%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png  

fKEe2MpbZ%2F%2Fd1pDdJAd4yw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngfKEe2MpbZ%2F%2Fd1pDdJAd4yw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

D3w9xB%2BL2c%2FBZ%2B6tnFW23Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngD3w9xB%2BL2c%2FBZ%2B6tnFW23Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 07:11 AM . Last Modified: ‎2024-03-04 10:59 PM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:11 AM . Last Modified: ‎2024-03-04 10:59 PM

Nice idea Terry, thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-01 07:10 AM . Last Modified: ‎2024-03-04 10:59 PM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:10 AM . Last Modified: ‎2024-03-04 10:59 PM

I don't have any good ideas for this. The only thing I can think of is that since the transfer switch will only change sources if the other source is "better", both UPSs switching back to AC power at the same time may cause the ATS to decide that neither source is good. If these are APC UPSs (and even if they aren't, but offer a similar option), you could try setting the "delay returning to utility power" to different lengths of time on the two UPSs. If one returns immediately and the ATS doesn't like that, it will stay/switch to the UPS that is still on batteries. By the time that second UPS then switches back to AC power, the first UPS should be supplying power that the ATS is happy with. I think the ATS will try to avoid switching sources more often than 30 seconds, so a 0-second delay on one UPS and a 60-second delay on the other might do the trick.

BTW, the log you posted seems to be from 10+ years ago. If that is because the time is not set on the ATS, you probably want to configure it to use an NTP server (or at least manually set the date / time) - it will make it a lot easier to correlate items in the event log with timestamps from other equipment. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:10 AM . Last Modified: ‎2024-03-04 10:59 PM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:10 AM . Last Modified: ‎2024-03-04 10:59 PM

Hello,

When you walked over to the ATS, the output LED was off? This should typically never happen but I have seen it before - where the ATS needs manual intervention to turn the output back on. I have seen it in situations like what Terry described where both sources are potentially bad at the same time.

It would be helpful to see the full logs/configuration, if you could share event.txt, data.txt, and config.ini files from the AP7752. Instructions here on downloading those -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:10 AM . Last Modified: ‎2024-03-04 10:59 PM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:10 AM . Last Modified: ‎2024-03-04 10:59 PM

The LED was on and the display showed zero amperes. I'll get the ;logs as soon as possible, thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:11 AM . Last Modified: ‎2024-03-04 10:59 PM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:11 AM . Last Modified: ‎2024-03-04 10:59 PM

Nice idea Terry, thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of