I have APC-750 UPS monitored by PowerChute, and scheduled to run self-test every weekend. It's been several weeks keep sending a fail self-test message and need battery replacement. I have just replaced the battery couple of months ago. However, every time it send the fail self-test, I try to run the self-test manually, and it comes back to on-line. Any idea why is this happened or suggestion to make the message sends the right one? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:32 PM . Last Modified: 2024-02-14 11:49 PM
did the RBC have a serial number on it so we can check its age?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:31 PM . Last Modified: 2024-02-14 11:49 PM
Good day Ahar,
Aside from the message that you receive thru PowerChute, I would like to check if the UPS itself shows a solid red replace battery indicator? Also, have you tried changing the USB/Serial cable?
Was it replaced with a genuine APC battery as well?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:31 PM . Last Modified: 2024-02-14 11:49 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:31 PM . Last Modified: 2024-02-14 11:49 PM
Yes, it shows a solid red replace battery indicator. I replaced it with genuine APC battery, last time.
Never tried to change the monitoring cable, though.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:31 PM . Last Modified: 2024-02-14 11:49 PM
When was the last time that you have changed the battery? Because if the message is accompanied by a solid replace battery led it only means that the battery is bad and needs to be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:32 PM . Last Modified: 2024-02-14 11:49 PM
did the RBC have a serial number on it so we can check its age?