APC 3000 - managing with serial port

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 3000 - managing with serial port
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

0 Likes
3
8816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

APC 3000 - managing with serial port

I've got an Smart-UPS 3000 with a serial port connection. I can't find any info on how to monitor the UPS using this connection. Ideally, I'd like to install powerchute business on a server and hook the UPS up to it to monitor. Can the serial port be used in this way? (just like the USB to RJ45 connection)

TIA!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

0 Likes
0
8803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

Hi again,

If it is a DB-9 port, it is an older UPS platform. You'd need the 940-0024 or 940-1524 serial cable. Connecting a standard cable could cause the UPS to turn off or do other actions so make sure to verify it is an APC cable and look for the part number on one of the connector ends. Here is the cable, it should've come with your UPS in the box along with that USB cable. Buy UPS Communications Cable Smart Signalling - Technical Specifications and Information | APC (the only difference in the two part numbers I gave are the lengths) - 6ft versus 15ft.

If this UPS has the DB-9 port, and you have tried USB at some point (whether successful or not), I'd braindead the UPS to reset the serial port. This will give you the best change of PowerChute Business Edition auto-detecting the UPS as present but it does allow you to specify the communication port on your computer the UPS cable is connected to.

To braindead, turn off the UPS and remove any cables you may have connected down. Then remove the AC power from the UPS. Find the (o) off button on the front panel and hold it down for a few seconds until you hear a click and/or see the front panel LEDs flash. Then, you can plug it back in and turn the UPS back on and the serial port should be active.

Let me know if there are further questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

0 Likes
0
8803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

Yes, you can do this. Do you know the exact model/SKU of the UPS from the white sticker on the back? I ask because this will determine what serial cable you should use. Or, if you can tell me if it is a DB-9 or RJ-45 type serial port, that will help. It will also determine what you need to get serial communications working. If it is an older UPS and you've already used USB, for example, the serial port is "dead" and you'll need to reset the UPS to make it work again. If it is a newer model, this won't be required.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

0 Likes
0
8803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

Thx for your reply!

It's a newer UPS and we haven't plugged anything in yet. It's a DB-9 port. Do you have a link to the correct DB-9 cable I need?

When I get the correct cable will the powerchute business ed. software automatically recognize it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

0 Likes
0
8804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:50 AM . Last Modified: ‎2024-03-05 12:10 AM

Hi again,

If it is a DB-9 port, it is an older UPS platform. You'd need the 940-0024 or 940-1524 serial cable. Connecting a standard cable could cause the UPS to turn off or do other actions so make sure to verify it is an APC cable and look for the part number on one of the connector ends. Here is the cable, it should've come with your UPS in the box along with that USB cable. Buy UPS Communications Cable Smart Signalling - Technical Specifications and Information | APC (the only difference in the two part numbers I gave are the lengths) - 6ft versus 15ft.

If this UPS has the DB-9 port, and you have tried USB at some point (whether successful or not), I'd braindead the UPS to reset the serial port. This will give you the best change of PowerChute Business Edition auto-detecting the UPS as present but it does allow you to specify the communication port on your computer the UPS cable is connected to.

To braindead, turn off the UPS and remove any cables you may have connected down. Then remove the AC power from the UPS. Find the (o) off button on the front panel and hold it down for a few seconds until you hear a click and/or see the front panel LEDs flash. Then, you can plug it back in and turn the UPS back on and the serial port should be active.

Let me know if there are further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore