Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

APC 3000 issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 3000 issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

0 Likes
5
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

APC 3000 issue

Greetings folks,

I hope I'm posting this to the appropriate group. If not, please let me know.

We have a pair of APC Smart - UPS 3000, firmware rev is ID18UPS 06.5. While performing some maintenance recently, we plugged in a Lenovo laptop running Windows 7 to the serial port of one of the APC units and it immediately shut down. We were able to reproduce the problem after bringing it back online. It seems the laptop is sending a shutdown/terminate signal to the APC unit upon connection??!

Is this a known problem? Firmware update needed? Very strange indeed. We are using 3rd party software/device for the serial port, a USB serial port adapter from Keyspan TripLite.

Thank you in advance for any info.

BuddyD

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

Hi

940-0299 is used for direct access to the AP9630 Network Management Card and is only intended for serial communication/configuration to the network card.

What are you trying to do via serial cable by connecting a laptop? If you have a Network Management Card, you'd likely want to set that up and then access it over the network for management and monitoring of the UPS. If you need computers/servers to gracefully shutdown, you'd then use PowerChute Network Shutdown software on them and they would talk over the network to the Network Management Card to keep an eye on UPS status, etc. Typically, you would not be connecting a serial cable beyond briefly for configuring the AP9630 if you needed to via that method and then 940-0299 should be removed.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

Greetings folks,

I hope I'm posting this to the appropriate group. If not, please let me know.

We have a pair of APC Smart - UPS 3000, firmware rev is ID18UPS 06.5. While performing some maintenance recently, we plugged in a Lenovo laptop running Windows 7 to the serial port of one of the APC units and it immediately shut down. We were able to reproduce the problem after bringing it back online. It seems the laptop is sending a shutdown/terminate signal to the APC unit upon connection??!

Is this a known problem? Firmware update needed? Very strange indeed. We are using 3rd party software/device for the serial port, a USB serial port adapter from Keyspan TripLite.

Thank you in advance for any info.

BuddyD

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

Hello,

APC UPSs require proprietary serial cables. When you use standard serial cables, this is the type of behavior you see because of the different pinout in the cable.

It is OK to use the serial to USB adapter but we need to identify the part number of the serial cable you're using between that and the UPS. It should be a DB-9 to RJ-45 cable and the RJ-45 end connects to the port labeled SERIAL on the UPS and the DB-9 to the serial/DB-9 side to your USB to serial adapter. The DB-9 connector on the UPS cable should have a part number engraved into it. Can you confirm what you see there? This UPS requires 940-0625 or 940-1525.

You should have it set up such as Laptop USB port->USB to serial adapter->APC specific serial cable DB-9 side->RJ-45 connector to UPS serial port.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

Thank you both Bill P and Angela N !

I looked into this a bit further, we have a network card ( 9630, I believe ) on the units. I also discovered a "strange" looking cable connected to one of the units 940-0299A (?). This is plugged in to a single pin port labelled console.

Is this the correct cable to use for direct access, if necessary?

Thanks again to both of you.

Buddy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

Hi

940-0299 is used for direct access to the AP9630 Network Management Card and is only intended for serial communication/configuration to the network card.

What are you trying to do via serial cable by connecting a laptop? If you have a Network Management Card, you'd likely want to set that up and then access it over the network for management and monitoring of the UPS. If you need computers/servers to gracefully shutdown, you'd then use PowerChute Network Shutdown software on them and they would talk over the network to the Network Management Card to keep an eye on UPS status, etc. Typically, you would not be connecting a serial cable beyond briefly for configuring the AP9630 if you needed to via that method and then 940-0299 should be removed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 AM . Last Modified: ‎2024-03-12 02:42 AM

Hi Angela,

Thanks again for the advice. Yes, we do have the units on the network and they are being monitored (SNMP) and are readily accessible. The serial/console access only comes into play in a worst case scenario but after further discussion here, we don't think it's really necessary. We were more concerned initially with the status of the units and perhaps thought we might have a misconfiguration on the network card.

Thanks again for all your help, much appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of