APC 3000 UPS, configuration shutdown NA?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 3000 UPS, configuration shutdown NA?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:03 PM . Last Modified: ‎2024-03-14 03:47 AM

0 Likes
8
1996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:03 PM . Last Modified: ‎2024-03-14 03:47 AM

APC 3000 UPS, configuration shutdown NA?

Hello

I have some problems with a APC 3000 UPS, that is acting wierd in the web-interface > UPS > configuration > shutdown.
The dropdowns which i can choose from(Low Battery Duration, Shutdown Delay, Minimum Battery Capacity and Return Delay), are all marked as NA, and i cannot pick other values as normal, do anybody know the solution to this problem?

Thanks

Martin

Message was edited by: Lorensen

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:46 AM

0 Likes
0
1995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:46 AM

"That just tells you Syracuse wasn't that Griffey Shoes good," Barkley retorted. There will probably be people Air Jordan Heels who agree with Barkley that only eight Big East teams belonged in the NCAA tournament Ken Griffey Shoes as a result of the conference's awful showing, but the truth is the league simply performed well below Air Max 24 7 expectations in single-elimination format. Based on their season-long body of work, it would have been very difficult to justify leaving Nike Air Yeezy out Connecticut, Villanova or Marquette, the teams that finished ninth, 10th and 11th in the Big East regular-season standings. Even Nike Dunk Heels though he had the more logical argument, Pitino didn't exactly help himself when he looked straight into the camera and guaranteed "Notre Dame will not lose" Sunday night against Florida State. The lesson here: Never pin your TV credibility to Notre Dame in the NCAA tournament and never argue with Barkley even when you're right.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:03 PM . Last Modified: ‎2024-03-14 03:47 AM

0 Likes
0
1995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:03 PM . Last Modified: ‎2024-03-14 03:47 AM

It's a: Smart-UPS RT 3000XL

I'm using a single network card, and there's no serial or USB cable in the UPS.

APP name and version: sumx, v3.5.5
AOS name and version: aos, v3.5.5

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:03 PM . Last Modified: ‎2024-03-14 03:47 AM

0 Likes
0
1995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:03 PM . Last Modified: ‎2024-03-14 03:47 AM

we'd also need to know the exact model of the UPS from the white sticker on the UPS if possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

0 Likes
0
1995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

Can you get the firmware information on the network card from the Administration -> General subtab and give us the (or a screenshot):

APP name and version (should be a three or four character name and version number)
AOS name and version (should be aos and a version number)

Are you using just this single network card, or do you have any extra accessory single/triple chassis hooked up to the UPS? Is there a serial or USB cable plugged into the UPS? If so, are you using PowerChute Business Edition on an attached server? What is the model and serial # of the network card installed in the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

0 Likes
0
1995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

ipickedawinna, are you saying that the difference is that one is UPSLink and the other is Microlink? In that case, an easy way to tell on the NMC web interface is whether the UPS page names start with "up", ie upshome.htm (upslink UPSes) or starts with a "ul", ie ulhome.htm (microlink UPSes).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

0 Likes
0
1995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

It is kinda difficult for me to find out, because the UPS is placed into a Windmill about 4000 Miles away.

Message was edited by: Lorensen

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

0 Likes
0
1995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

yes, thats good to know! thanks voidstar.

Lorensen, can you paste to us the hyperlink address (removing your IP) of the UPS tab for example?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

0 Likes
0
1995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:47 AM

I'm having a similar problem with my UPS
it's a SUA2200RM2U with an AP9606 Web/SNMP interface card

Firmware string is as follows.

American Power Conversion Web/SNMP Management Card AOS v3.2.6.b
(c) Copyright 2000 All Rights Reserved Smart-UPS & Matrix-UPS APP v3.2.6.a

can anyone help me with this unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:46 AM

0 Likes
0
1996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:04 PM . Last Modified: ‎2024-03-14 03:46 AM

"That just tells you Syracuse wasn't that Griffey Shoes good," Barkley retorted. There will probably be people Air Jordan Heels who agree with Barkley that only eight Big East teams belonged in the NCAA tournament Ken Griffey Shoes as a result of the conference's awful showing, but the truth is the league simply performed well below Air Max 24 7 expectations in single-elimination format. Based on their season-long body of work, it would have been very difficult to justify leaving Nike Air Yeezy out Connecticut, Villanova or Marquette, the teams that finished ninth, 10th and 11th in the Big East regular-season standings. Even Nike Dunk Heels though he had the more logical argument, Pitino didn't exactly help himself when he looked straight into the camera and guaranteed "Notre Dame will not lose" Sunday night against Florida State. The lesson here: Never pin your TV credibility to Notre Dame in the NCAA tournament and never argue with Barkley even when you're right.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.